Discuss What sub base for tiles in the DIY Tiling Forum area at TilersForums.com.

Reaction score
3
Points
88
Location
Sheffield
Hi. I'm after some advise. I am shortly going to be ripping out water damaged patchy chipboard flooring in our utility room. We have purchased the floor tiles ready for this. Can I use 25mm WBP ply fixed to the joists with noggins on the ends and tile straight to this or is this wrong. Any advise much appreciated.
 

Ajax123

TF
Esteemed
Arms
Reaction score
931
Points
1,213
Location
Lincolnshire
Use 18mm ply but then overboard using 6mm cement based backer boards.
 
W

Waluigi

Quite unusual on a downstairs having chipboard with joists. Actually good point and worth checking
 
Reaction score
3
Points
88
Location
Sheffield
Hi, thanks for your replies. It is a ground floor extension that was done by previous owner. It has 6x2 joists with a 12" space to the ground with supports spaced out. Sorry I'm not sure is this classed as floating. The room is only 2.1 x 2.8.
 

Ajax123

TF
Esteemed
Arms
Reaction score
931
Points
1,213
Location
Lincolnshire
lots of floating floors are placed on battens which to a novice could be mistaken for joists.
 
Reaction score
3
Points
88
Location
Sheffield
Thanks. I've just read something about sealing the underside of the ply. What's the reason for this and does the ply need priming for adhesive to bond to.
 
W

WetSaw

Thanks. I've just read something about sealing the underside of the ply. What's the reason for this and does the ply need priming for adhesive to bond to.

Ply needs overboarding for adhesive to bond to. Don't stick tiles straight on to ply, not unless you want to be doing it again very soon!
 
W

Waluigi

Just had a lengthy and detailed reply typed out. Decided to delete it. Sad state of affairs. My apologies to Craigo. I hope you find the information you’re looking for. Over and out.
 

Bond

TF
Arms
Reaction score
270
Points
518
Location
Highland
Aye it’s a good idea to seal the underside of the ply as sub floor areas can have a high relative humidity, and by sealing with SBR or similar it will help prevent the ply from absorbing moisture etc.
 
J

J Sid

British Standard states
6.3.4.2 New timber bases New timber bases should be constructed with noggings between the joists. Water and boil proof (WBP) exterior grade plywood of 15 mm minimum thickness should be screwed to both joists and noggings at 300 mm maximum intervals. The lower face and edges of plywood should be sealed against the ingress of moisture using preferably non-aqueous sealers, e.g. polyurethane varnish, or styrene butadiene rubber, to prevent distortion by changes in atmospheric humidity before being screwed down. All junctions between boards should be supported by noggings or joists.
 

Reply to What sub base for tiles in the DIY Tiling Forum area at TilersForums.com

There are similar tiling threads here

Hi! I'm looking for some advice, I have laid some SLC (Mapei 1210) in our conservatory in...
Replies
5
Views
565
I had a small leak in the main water line before the stop tap in my 1950s house. The copper pipe...
Replies
1
Views
613
Hi all. Just wanting some advice and wondering what the pros in here are using nowadays for...
Replies
2
Views
547
Good morning all. After a little advice. I'll post pictures a bit later. However.... The...
Replies
6
Views
780
    • Like
Bathroom floor. I would be grateful for advice on how to prepare my bathroom sub floor ready for...
Replies
1
Views
428

Advertisement

New Tiling Questions

Replies you've not seen

Top