The cheapest solution to this problem is to pull the screed up (2-3hours work) get a competent plumber/heating engineer involved, rescreed and tile. Job done!
 

Ajax123

TF
Esteemed
Arms
Reaction score
931
Points
1,213
Location
Lincolnshire
The cheapest solution to this problem is to pull the screed up (2-3hours work) get a competent plumber/heating engineer involved, rescreed and tile. Job done!
Not necessarily Lee. it depends largely on the area to be treated. As I said it is more dependent on depth than anything else. if you take up the screed you are likely to lose the pipes and possibly the insulation as well which bumps up the price. An epoxy repair compound can often be the best and most cost effective repair to these sorts of scenarios. That said if it were in my house, not that such a rubbish screed would ever find house room in my house, I would indeed want it removed and replaced but at the builder/screeders cost. The issue with that in this instance is I suspect the screeder is long gone
 

Chalker

TF
Arms
Reaction score
628
Points
1,058
Location
Tadcaster
Irrespective of the screed, the pipework needs controlling. Having no mixing set/manifold, will destroy anything that's laid on it.
 

Sean Kelly

TF
Arms
Reaction score
647
Points
1,068
Location
Ruislip
Many thanks Alan and lads, all I can do is report this discussion back to my Doctor. Shame we can't X-ray the floor!!

I would also like to know the outcome of this issue. So will request that she keeps me in the loop.

Cheers
Sean
 

Chalker

TF
Arms
Reaction score
628
Points
1,058
Location
Tadcaster
You can, well sort of.
I have a FLIR camera for my phone. Very handy to trace pipework in floors.

161117094344.jpg
 

Ajax123

TF
Esteemed
Arms
Reaction score
931
Points
1,213
Location
Lincolnshire
Irrespective of the screed, the pipework needs controlling. Having no mixing set/manifold, will destroy anything that's laid on it.
Missed that....you're completely correct. Running an underfloor heating sysem too hot is also a health risk. It has been linked in some studies to thrombosis. Maximum surface temperature should be 27C with an anticipated surfacd temperature around 22 to 23C. This would require a flow temperature of around 40 to 45 in sand cement. Radiators tend to run at 60+. Running radiator temperature flows will yeild a temperature closer to 45 to 50C in sand cement. This can be dealt with in small areas using a Return temperature limit valve but these are not suitable for anything over about 15m2
 

John Benton

TF
Arms
Reaction score
2,214
Points
1,138
Location
Leeds
The top of the screed does looks very sandy, no way should you be able leave finger marks when scraping the surface. I wouldn't really be happy putting any type of floor covering over that screed combined with the heating system.

I'm also intrigued to know, when he called for an appointment, did you tell him there were no free times until 2 weeks on Thursday, and he would have to ring first thing in the morning?
 

Reply to Screed & wet UFH issues. in the Tiling on Underfloor Heating area at TilersForums.com

There are similar tiling threads here

    • Like
Bathroom floor. I would be grateful for advice on how to prepare my bathroom sub floor ready for...
Replies
1
Views
439
Hi all. Just wanting some advice and wondering what the pros in here are using nowadays for...
Replies
2
Views
564
Hi! I'm looking for some advice, I have laid some SLC (Mapei 1210) in our conservatory in...
Replies
5
Views
579
I had a small leak in the main water line before the stop tap in my 1950s house. The copper pipe...
Replies
1
Views
620
Please visit our sponsor websites, they keep the forum free to use!

Advertisement

New Tiling Questions

Replies you've not seen

Top