barno101

We are our wits end ,,
We had an Anhydrate Floor screed laid at 40 mm and was left for 6 weeks to dry ,, the problem we got is the tiler laid the porcelain tiles on the floor he primed it ,and use rapid set flexi adhesive, followed all the correct procedures .
The plumber ,then turned on the underfloor heating and left it on full blast and was on for a long time , he never raised it slowly like he should have day by day . now the tiles have lifted .
The plumbers says the floor wasn't dry enough and thats what caused them to lift .
but we are saying he should have turned it up slowly ..

Any advise please

Cheers
 
I

Ian

Could you give us a bit more information if possible please. Was the heating commissioned (turned on and run up/down) prior to tiling? Was the floor sanded to remove any laitence prior to tiling? What adhesive was used? How long after the tiling was completed was the heating turned on?
 
T

Time's Ran Out

It's always the plumbers fault! :smilewinkgrin:
Did you know all this information at the time and just let the professional handle it or is this information gleaned from forums such as this?
 
S

Stef

Could you give us a bit more information if possible please. Was the heating commissioned (turned on and run up/down) prior to tiling? Was the floor sanded to remove any laitence prior to tiling? What adhesive was used? How long after the tiling was completed was the heating turned on?

As said here a bit more info would help.
It doesn't sound great to be honest!!
 
B

barno101

All the latency was taken off ,,the tile adhesive was the one recommended by for these floors, BAL rapid set flexi as far as i know . the heating was turn on a bout 2 after tiling and it was put on full blast
 
J

Just Rizzle

I think there both to blame I never use cement based adhesives on anhidrite floor as there is always going to be a reaction. anofix by tilemaster my preferred choice ,I also never tile a floor befor its commissioned. why didn't your tiler recommend a decoupling mat. also your plumber should of known to slowly raise the floors temp.how big an area was it?
 
B

barno101

the area was 144m2,it was a new build house, there is a an ongoing argument that the plumber is saying the floor was not dry enough ,, but we are saying if the heating was raised gradually as it is supposed to ,then the tile may have not come up ,, but if the floor was still damp the plumber is saying that ,that is the problem ...
there is only about 60% of the tiles that have com loose ,, and the grout has cracked where there is a congregation of pipes on the underfloor heating as it goes into the manifold s
There are three manifolds in the house
 
B

barno101

he prepped the floor properly i.e. two coats of primer after cleaning the floor area of any residue ,,the tiler has done everything right .. the plumber is saying that the floor area was still damp ...
 

Ajax123

TF
Esteemed
Arms
Reaction score
931
Points
1,213
Location
Lincolnshire
so many errors in one small floor... Where to begin.
 

Reply to anhydrite floor screed in the Australia Tiling Forum area at TilersForums.com

There are similar tiling threads here

I had a small leak in the main water line before the stop tap in my 1950s house. The copper pipe...
Replies
1
Views
658
    • Like
Bathroom floor. I would be grateful for advice on how to prepare my bathroom sub floor ready for...
Replies
1
Views
508
Hi! I'm looking for some advice, I have laid some SLC (Mapei 1210) in our conservatory in...
Replies
5
Views
626
Posting a tiling question to the forum? Post in Tilers' Talk if you are unsure which forum to post in. We'll move it if there's a more suitable forum.
Please visit our sponsor websites, they keep the forum free to use!

Advertisement

New Tiling Questions

Replies you've not seen

Top