barryrobins

Hi - can anyone offer any advice. We have water u/f heating throughout house and had upstairs bathroom made into wetroom. Chipboard flooring, then dietra matting, then tiles. 6 months later, tiles cracking across floor. Have now been told that dietra matting not recommended for any u/f water heating and that even if we replace chipboard flooring with plywood, then this still may not work. All to do with joists not having "noggings" as a result of u/f heating pipes.

Don't know what to do now - cusion floor seems only alternative but this would obviously be above level of the shower flooring (which incidentially hasn't shown any signs of movement)
and completely ruin the look of the bathroom.

Any advice welcome!
 
M

Max@ableskills

Hi - can anyone offer any advice. We have water u/f heating throughout house and had upstairs bathroom made into wetroom. Chipboard flooring, then dietra matting, then tiles. 6 months later, tiles cracking across floor. Have now been told that dietra matting not recommended for any u/f water heating and that even if we replace chipboard flooring with plywood, then this still may not work. All to do with joists not having "noggings" as a result of u/f heating pipes.

Don't know what to do now - cusion floor seems only alternative but this would obviously be above level of the shower flooring (which incidentially hasn't shown any signs of movement)
and completely ruin the look of the bathroom.

Any advice welcome!

Hi and welcome to the forum. It sounds like your floor maybe suffering from deflection issues. Basically from what you have said the floor was not strong enough because it did not have enough noggins.

I take it the floor was taken up, underfloor heating installed, chipboard put back down, then ditra, then tile.

If so when the floor was up more noggins needed to be installed.

No easy solution to this i am afraid
 
B

barryrobins

Thanks for comments so far. In fact Schluter told me yesterday the matting is unsuitable for WATER underfloor heating but largely the problem is the unstable flooring. We are thinking of replacing chipboard with ply but really concerned that we'll just have the same problem in six months time. Is it possible to put more noggins in the joists? Sorry to be so uninformed about this - the builder who renovated the house put in the flooring and we employed a tiler to lay the matting and tiles. Its our opinion that assuming we know nothing about tiling, he should have advised us against laying tiles on chipboard over flooring that is unstable.
 
B

barryrobins

icon1.png
Re: Water underfloor heating, ceramic tiles


Thanks for comments so far. In fact Schluter told me yesterday the matting is unsuitable for WATER underfloor heating but largely the problem is the unstable flooring. We are thinking of replacing chipboard with ply but really concerned that we'll just have the same problem in six months time. Is it possible to put more noggins in the joists? Sorry to be so uninformed about this - the builder who renovated the house put in the flooring and we employed a tiler to lay the matting and tiles. Its our opinion that assuming we know nothing about tiling, he should have advised us against laying tiles on chipboard over flooring that is unstable​
 

Ajax123

TF
Esteemed
Arms
931
1,213
Lincolnshire
Schluter sell Ditra Matting specifically for warm water underfloor heating systems so how on earth can they be saying it is not suitable. Either you are mis interpretting their comments or you are not telling us something about your floor.

Did you tell the builder that the floor was to be used as a wet room and to be tiled. Perhaps he has some questions to answer

I can't see much option here but to remove the floor down to the joists and replacing it with more suitable materials. Whilst I agree that deflection is likely to be the primary cause there are other things with this floor which could contribute e.g. chip board swelling due to water ingress, excessive thermal expansion due to high temperatures are 2 which spring to mind.

I cannot see any reason why Noggins can't be placed between the joists due to underfloor heating pipes. IN fact these would give you something to rest the pipes and assuming you have used them the diffuser plates on.
 

Reply to Water underfloor heating, ceramic tiles in the UK Tiling Forum area at TilersForums.com

There are similar tiling threads here

I had a small leak in the main water line before the stop tap in my 1950s house. The copper pipe...
Replies
1
Views
777
Hello there, Relatively recently we had a new en-suite fitted (complete rip out of the old...
Replies
5
Views
2K
Posting a tiling question to the forum? Post in Tilers' Talk if you are unsure which forum to post in. We'll move it if there's a more suitable forum.
Please visit our sponsor websites, they keep the forum free to use!

Advertisement

Replies you've not seen

You're browsing the UK Tiling Forum category on TilersForums.com, the tile advice website no matter which country you reside.

Top