Hi all,
Ive been asked to lay limestone to a new extension, it has a main room 11 x 5m with smaller rooms off.
At present no expansion joints in slab and they say they are going to grind 8mm deep joint in middle of room and in doorways!
In my mind 8mm won't achieve anything ? I am proposing joints in stone in doorways and wanted one across middle of main room all fitted on decoupler.
However i am nervous that concrete has no full depth joints.
Any thoughts please?
 
L

LM

Hi all,
Ive been asked to lay limestone to a new extension, it has a main room 11 x 5m with smaller rooms off.
At present no expansion joints in slab and they say they are going to grind 8mm deep joint in middle of room and in doorways!
In my mind 8mm won't achieve anything ? I am proposing joints in stone in doorways and wanted one across middle of main room all fitted on decoupler.
However i am nervous that concrete has no full depth joints.
Any thoughts please?
Is there under floor heating in the screed?
 

Ajax123

TF
Esteemed
Arms
Reaction score
931
Points
1,213
Location
Lincolnshire
Any cut joints are for shrinkage control unless they are made to the full depth. Shrinkage joints should be a minimum of 1/3rd of the total depth of the slab. 8mm deep joints are pointless
 

SteveH

TF
Reaction score
0
Points
36
Location
Framingham
Any cut joints are for shrinkage control unless they are made to the full depth. Shrinkage joints should be a minimum of 1/3rd of the total depth of the slab. 8mm deep joints are pointless
Thanks, yes I thought as much, probably more to appease the customer who asked about them whilst not wanting to nip a pipe! Shouldn’t there be full joints in slab if heating is zoned?
 

SteveH

TF
Reaction score
0
Points
36
Location
Framingham
Are there Brit standards for expansion joints in concrete with UFH and zones?There are none, manufacturer only says typically there should be and builder who fitted UFH etc says its screed suppliers fault!
 

Reply to Fitting Limestone to new concrete flow screed 80mm, wet UFH and main room is 11m x 5m! in the The Welcome Forum area at TilersForums.com

There are similar tiling threads here

Good morning all. After a little advice. I'll post pictures a bit later. However.... The...
Replies
6
Views
787
Hi all. Just wanting some advice and wondering what the pros in here are using nowadays for...
Replies
2
Views
561
I had a small leak in the main water line before the stop tap in my 1950s house. The copper pipe...
Replies
1
Views
616
Hi! I'm looking for some advice, I have laid some SLC (Mapei 1210) in our conservatory in...
Replies
5
Views
573
Please visit our sponsor websites, they keep the forum free to use!

Advertisement

New Tiling Questions

Replies you've not seen

Top