I have been to see a job last week,90m2 ground floor kitchen/conservatory. It will be,when it is laid, a 60mm sand/cement screed over wet ufh over insulation over a block and beam floor.
Unfortunately the lady of the house was not aware of the drying times for the screed and was expecting her dream kitchen/conservatory to be done and dusted before Christmas. I have told her want the screed and the ufh requires prior to commencing tiling,but she has come back to me with this scenario from the builder/screed company........
......2 days after the screed has been laid start the ufh heating at its lowest level for a week,then increase the heating by 1 degree per day,up to normal operating temperature.
Has anyone heard of this procedure being correct or have they got their facts slightly wrong/stretching the truth?
P.S would a screed this size require reinforcing mesh?
Thanks in advance Wrighty
I have been to see a job last week,90m2 ground floor kitchen/conservatory. It will be,when it is laid, a 60mm sand/cement screed over wet ufh over insulation over a block and beam floor.
Unfortunately the lady of the house was not aware of the drying times for the screed and was expecting her dream kitchen/conservatory to be done and dusted before Christmas. I have told her want the screed and the ufh requires prior to commencing tiling,but she has come back to me with this scenario from the builder/screed company........
......2 days after the screed has been laid start the ufh heating at its lowest level for a week,then increase the heating by 1 degree per day,up to normal operating temperature.
Has anyone heard of this procedure being correct or have they got their facts slightly wrong/stretching the truth?
P.S would a screed this size require reinforcing mesh?
Thanks in advance Wrighty