What insulation was laid and what depth. My guess is that it's an indulation issue rather than a malfunctioning most issue
Discuss Electric ufh not reaching desired temperature in the Tiling on Underfloor Heating area at TilersForums.com.
Sorry to enter late in this thread but a question I have is, is the sensor over the timber floor side or the concrete floor side? If it's over the timber floor side then that area of floor around the sensor could be reaching the set temperature before other floor areas, such as the concrete floor area, and then switching of the system as programmed. Unfortunately the floor sensors only sense the immediate area where the sensor is placed and cannot sense the temperature on the other side of the floor. Dependant upon the programmer and where it is mounted ie. Does the programmer have the option to sense air temperature instead of floor temperature? And is the programmer mounted within the same roon as the underfloor system?
If the answer to both is yes then you could disconnect the floor sensor and use the programmer to sense air temperature instead. Even if only to see if it works any better that way.
The programmers that I use have both options and we mostly use the air temperature option, even though we still fit the floor sensor as an option to our customers if they wanted to go that route instead.
So we isolated the mat which is on the timber floor side, disconnected the sensor which only left the mat in the concrete floor side connected for approx 6 hours.
6 hours later the floor is barely warm! you can just about feel some warmth on the tiles
Should i leave it on longer? If so is there any risk of damage, overheating etc given that the floor sensor has been disconnected
The thermostat doesn't have an air sensor
Okay. So heating a concrete floor from cold could easily take a day or so before you may feel any serious heat through the face of the tiles. Obviously the time scale is dependant upon the floor / insulation make up below the tile (how thick is the insulation / how far below the tile is the insulation / how cold was it before switching the underfloor on etc).
You say that you are starting to feel heat at around the 6 hour point which is a good sign as it shows that it is actually heating.
You need to keep the system switched on a lot longer yet but say every hour just carry out a check of the surface temperature of the tiles in various places over the floor. If you use the back of your hand to check this and not your palm then you will have a better idea of just how warm or hot it is getting. If it feels like a snugly / comfortable warm temperature then that should be as far as it needs to get. If the temperature is really getting quite hot or too warm to be comfortable on the back of your hand then it is going too far and needs to be turned off. The temperature shouldn't be allowed to go above around 55deg's 'C' as there is a risk then of breaking down the screed below. Trust me here though, even 40deg's on the back of your hand will feel uncomfortable!
so, in carrying out the above you will confirm that that part of the system is functioning correctly.
You didn't say in which part of the floor the sensor was placed?? Was it the timber side or the concrete side??
Obviously in all of this, do be aware and remember that you now have no sensor connected so make sure you turn off the system before going to bed this evening if you carry out the above first thing in the morning.
Let me know how you get on.
I forgot to mention that the advice I have given is just an exercise purely to confirm that the system functions and will get to a temperature.So we isolated the mat which is on the timber floor side, disconnected the sensor which only left the mat in the concrete floor side connected for approx 6 hours.
6 hours later the floor is barely warm! you can just about feel some warmth on the tiles
Should i leave it on longer? If so is there any risk of damage, overheating etc given that the floor sensor has been disconnected
The thermostat doesn't have an air sensor
I forgot to mention that the advice I have given is just an exercise purely to confirm that the system functions and will get to a temperature.
Because the sensor has been disconnected there is no over temp protection so don't leave the system running constantly unmonitored otherwise there is a risk of cooking the underfloor system.
Okay. So on the concrete side you have no insulation which means your heat losses will be very high and so warm up times will be much longer as you are heating a concrete slab instead of reflecting the heat upwards and out through the floor. It's a shame this wasn't considered as even a 6/8mm sheet of insulation would have made a big difference here so your losses would have been far less and you would have felt the benefits far quicker. This will also have an impact on your energy bill too!Cheers I'll do the above and report back
The floor setup is as follows
On the timber floor side it was overlaid with 6mm cement boards, primed and the mat laid on top followed by the adhesive and tiles
The floor sensor was positioned 300mm in between the heating cables on the timber floor side
The concrete side no insulation was laid as this would have increased the height of the floor. the floor was levelled using levelling compound which also encased the underfloor heating mat, followed by the adhesive and tiles.
The mat is 2mm thin 200w per sqm cable mat