Discuss UFH - whole mat is not heating up. in the Tiling Forum at TilersForums; Hi, i am hoping someone can help me, as this is my first post but in desperate need of some advice. we have installed electric ufh and had it tiled, ...
          
  1. #1
    New TilersForums Contributor ianmorrison9's Avatar
    Join Date
    Nov 2010
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0
    Posts

    Default UFH - whole mat is not heating up.

    Hi,

    i am hoping someone can help me, as this is my first post but in desperate need of some advice.

    we have installed electric ufh and had it tiled, but when installing we to remove the cable from the mat and coil it around to fit in the remaining space. The mat was tested before tiled and everything was working.
    However now its been tiled the area in the corner where there is more than normal amount of cable (it hasn't touched or crossed) it is very hot, but the rest of the mat does not seem to be heating anywhere near the amount it should.
    Are electrician thinks that the heat may be getting pulled to the area of most cable and missing the beginning of the mat out? is this possible and if so what options do i have? the area that isn't heating does not feel like we have any underfloor heating which is very disappointing.
    We have spoke to the suppliers and they advised not to shorten the cable, but is this them just covering themselves, because are electrician thinks it could work by not pulling as much power to that area? Has anyone ever shortened or cut their mat cables.

    the area that isn't warming as efficiently does have a poor sub floor compared to the rest of the room, could this have anything to do with it also?

    any help and advice is greatly appreciated?


    Ian

  2. #2
    TilersForums Trusted Member

    nybor62's Avatar
    Join Date
    Jun 2007
    Location
    rotherham
    Posts
    3,622
    Thanks
    908
    Thanked 674 Times in 578
    Posts

    Default Re: UFH - whole mat is not heating up.

    did you use insulation boards you could be loosing all the heat into the floor , thus not generating up into the tile
    .07429209003 ROB
    tilers in rotherham nation wide service
    http://www.rjw-tilingspecialist.co.uk

  3. #3
    Tilers Forums Arms Member
    diamondtiling's Avatar
    Join Date
    Jun 2009
    Location
    cheshire
    Posts
    6,859
    Thanks
    4,735
    Thanked 3,022 Times in 1,991
    Posts

    Default Re: UFH - whole mat is not heating up.

    Your electrician sounds like a bit of a chancer, is he qualified? You cannot shorten the cable and it sounds as though it has been wrongly installed, the minimum gap is usually 55mm and you should not go below this. Have you installed the probe near to this excess of wires?

  4. The Following User Says Thank You to diamondtiling For This Useful Post:

    timeless john (26-11-2010)

  5. #4
    TilersForums Trusted Member

    Stewart's Avatar
    Join Date
    Aug 2010
    Location
    Dunfermline.
    Posts
    4,747
    Thanks
    437
    Thanked 1,203 Times in 965
    Posts

    Default

    Electrician doesn't know what he's talking about. You will have a hot spot due to the amount of cable in the one area as there is more cable to heat a smaller area and due to this, you will be unable to get a evenly heated floor. Also, as above, if the probe is in this area, it will cause the same problem, as the hotspot area will heat up quicker

    You could try changing the setting on the thermostat to room temp only and see how it heats up then.
    "The early bird catches the worm.... but it's the second mouse that gets the cheese"

  6. #5
    Administrator


    Dave's Avatar
    Join Date
    May 2007
    Location
    County Durham
    Posts
    54,472
    Thanks
    9,718
    Thanked 14,142 Times in 9,989
    Posts
    Blog Entries
    1

    Default Re: UFH - whole mat is not heating up.

    The coiled section is creating a hot spot and will burn out eventually.. it should not have been installed if too long.

  7. #6
    Tilers Forums Arms Member andy8758's Avatar
    Join Date
    Mar 2010
    Location
    Somerset
    Posts
    448
    Thanks
    36
    Thanked 128 Times in 96
    Posts

    Default Re: UFH - whole mat is not heating up.

    Quote Originally Posted by ianmorrison9 View Post
    Hi,

    we have installed electric ufh and had it tiled, but when installing we to remove the cable from the mat and coil it around to fit in the remaining space. The mat was tested before tiled and everything was working. All you test is that the cable has a set resistance (as described in the instructions). This measurement lets you know that the cable is undamaged - it does not tell you that everything is working.
    However now its been tiled the area in the corner where there is more than normal amount of cable (it hasn't touched or crossed) it is very hot, but the rest of the mat does not seem to be heating anywhere near the amount it should. With the cable installed too close to itself, it is heating itself - i.e. overheating and ultimately it could burn the cable out - this is a fire risk and it must not be used until that fault is rectified.
    Are electrician thinks that the heat may be getting pulled to the area of most cable and missing the beginning of the mat out? is this possible and if so what options do i have? the area that isn't heating does not feel like we have any underfloor heating which is very disappointing. No (properly qualified) electrician would give you that advice. Electricity flows through the cable, and the flow causes the cable to become hot - it does not miss the sparser areas to reach the denser areas - this is utter rubbish.
    We have spoke to the suppliers and they advised not to shorten the cable, but is this them just covering themselves, because are electrician thinks it could work by not pulling as much power to that area? Has anyone ever shortened or cut their mat cables. The correct way to install UFH is to accurately measure out the (0.5m) widths of the mat, across the room, and to order no more than that length - i.e. order a smaller floor area not a larger - then you have to plan where not to lay the mat, i.e. where you can live with a cold floor area.

    the area that isn't warming as efficiently does have a poor sub floor compared to the rest of the room, could this have anything to do with it also? The cable heat radiates evenly in all directions from the cable. If you lay it on concrete, it is putting as much effort uin heating the concrete as it does heating the tile. So you should lay the cable on insulation board (laid on top of the concrete) - this then reflects the radiated heat up through the tile, and stops the cable heating the concrete (or wood) floor.

    any help and advice is greatly appreciated? I am sorry but you must remove the tiles and UFH mat and start again.


    Ian
    Always read the instructions and follow them exactly - hope the above advice is followed - I know it is not helpful to you - but you cannot use the UFH as installed because of the risk of overheating of the cable.
    Last edited by andy8758; 26-11-2010 at 06:57 PM.

  8. #7
    Dan
    Dan is offline
    Tilers Forums Admin Dan's Avatar
    Join Date
    Apr 2006
    Location
    Staffordshire, UK
    Posts
    19,268
    Thanks
    7,724
    Thanked 5,039 Times in 2,887
    Posts
    Blog Entries
    6

    Default Re: UFH - whole mat is not heating up.

    Or just tile over it all again starting with insulation, then the right sized mat, and then tile. Cheaper than pulling it all up and redoing I'd guess.
    Dan
    TilersForums.co.uk Owner
    The UK's biggest Tiling Forum

    Like TF? Try our other forums: The UK's biggest Electrical Forum, The UK's biggest Plumbing Forum, The UK's biggest Flooring Forum. Some newer trade-related forums; Plastering Forum, Building Forum, Decorating Forum.
    Follow TilersForums on Twitter.


  9. #8
    jay
    jay is offline
    TilersForums Trusted Member

    jay's Avatar
    Join Date
    Apr 2009
    Location
    Tasmania
    Posts
    8,022
    Thanks
    3,968
    Thanked 1,990 Times in 1,587
    Posts

    Default Re: UFH - whole mat is not heating up.

    as above would be interested to know were probe was positioned and how

  10. #9
    New TilersForums Contributor ianmorrison9's Avatar
    Join Date
    Nov 2010
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0
    Posts

    Default Re: UFH - whole mat is not heating up.

    Hi,

    thanks so far for the replies, thought i'd best respond and provide some more information.

    The hotspot is nowhere near the probe.

    the room (kitchen/diner) has 2 mats, the larger mat in the dining area is on backer boards and heats up evenly, the smaller mat in the kitchen area is only on a 1mm mat (new product from tiling shop) as the levels were different so couldn't fit backer board, the excess wire from this mat runs around part of the perimeter infront of the patio doors (will this be cooling this area down) and into the corner were the hotspot is.

    surely people order larger size mats than they need and install them with extra wires in one area. how likely is it to overheat, it is probably covering an area of no more than 0.5sqm. (if that)

    is taking up the tiles covering the small mat and replacing the only option, i am really worrying about this overheating, but how likely is this, also the cost of taking up the tiles and replacing is going to be significant (they were very expensive tiles)

    how easy are tiles to take up and whats the likelyhood of taking them up without breaking them?!

    any responses and advice would be greatly appreciated.


    Ian

  11. #10
    Tool Hound


    Sir Ramic's Avatar
    Join Date
    Jan 2008
    Location
    Stourbridge, West Midlands
    Posts
    16,535
    Thanks
    1,471
    Thanked 5,604 Times in 3,566
    Posts
    Blog Entries
    2

    Default Re: UFH - whole mat is not heating up.

    It will depend on how well the tiles were fixed and how long they have been laid.
    Where about in the country are you?
    Wall and floor tiler in the West Midlands, Dudley, Stourbridge. www.nptiling.co.uk

  12. #11
    New TilersForums Contributor ianmorrison9's Avatar
    Join Date
    Nov 2010
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0
    Posts

    Default Re: UFH - whole mat is not heating up.

    the tiles have been done for no more than 3 months, we are in Liverpool, think the tilers used plenty of adhesive!!!

  13. #12
    Tool Hound


    Sir Ramic's Avatar
    Join Date
    Jan 2008
    Location
    Stourbridge, West Midlands
    Posts
    16,535
    Thanks
    1,471
    Thanked 5,604 Times in 3,566
    Posts
    Blog Entries
    2

    Default Re: UFH - whole mat is not heating up.

    I would think that you wouldnt lift the tiles without breaking them.

    Only asked because I went to school with an Ian Morrison....its not you...lol
    Wall and floor tiler in the West Midlands, Dudley, Stourbridge. www.nptiling.co.uk

  14. #13
    Tilers Forums Arms Member andy8758's Avatar
    Join Date
    Mar 2010
    Location
    Somerset
    Posts
    448
    Thanks
    36
    Thanked 128 Times in 96
    Posts

    Default Re: UFH - whole mat is not heating up.

    Quote Originally Posted by ianmorrison9 View Post
    Hi,

    thanks so far for the replies, thought i'd best respond and provide some more information.

    The hotspot is nowhere near the probe. The wall thermostat can be set to measure from probe only, probe and air temp, air temp only, or not take account of temps at all. If the thermostat takes account of room temp - then the hotspot may be affecting that reading. In any event the hotspot is always going to be "hot" whereas a properly functioning ufn system will make the tile feel mildly warm to the touch - not hot.

    the room (kitchen/diner) has 2 mats, the larger mat in the dining area is on backer boards and heats up evenly, the smaller mat in the kitchen area is only on a 1mm mat (new product from tiling shop) as the levels were different so couldn't fit backer board, the excess wire from this mat runs around part of the perimeter infront of the patio doors (will this be cooling this area down) and into the corner were the hotspot is.

    surely people order larger size mats than they need and install them with extra wires in one area. how likely is it to overheat, it is probably covering an area of no more than 0.5sqm. (if that) - no never buy too much, always buy less than floor area - you really cannot place wires closer than manufacturers recommendations - generally that is at least 50mm from walls, obstructions and other cable. Your retailer should always recommend buying less.



    how easy are tiles to take up and whats the likelyhood of taking them up without breaking them?!

    any responses and advice would be greatly appreciated.


    Ian
    Ian, I am sorry but you really seem to have misinstalled this heating system. The flow of electricity generally generates heat. Electrical installations are governed by BS7671:2008 commonly called the 17th Wiring Regulations - one of the regs is that you must install the appliance/accessory/installation according to the manufacturers instructions. The regs also include common issues affecting the safety of electrical installations - one of which is to reduce the risk of fire caused by incorrect instalklation of electrical installations. If you have a fire in your home now - your insurance company may refuse to cover you because of this. From what you are telling us the installation is not doing what it should - so the safest thing to do is rip it out and install it correctly.

  15. The Following User Says Thank You to andy8758 For This Useful Post:

    Scott (02-12-2010)

Similar Threads

  1. 'Underfloor heating' off of central heating loop?
    By SJRuss in forum Electric Underfloor Heating
    Replies: 9
    Last Post: 22-09-2011, 05:01 PM
  2. Tiling on conc. underfloor heating floor before heating is turned on
    By patrickoconnell in forum Tile Adhesive, Grout and Substrate Preparation
    Replies: 13
    Last Post: 27-10-2010, 07:38 PM
  3. heating
    By Lee222 in forum Tiling Forum
    Replies: 3
    Last Post: 07-06-2010, 04:09 PM
  4. 1 week after tiling: UFH not on but central heating pipes heating tiles...
    By wilfredolimb in forum Electric Underfloor Heating
    Replies: 5
    Last Post: 03-12-2009, 11:43 AM
  5. Ribbon Underfloor Heating by AHT - Heating
    By Dan in forum Electric Underfloor Heating
    Replies: 35
    Last Post: 10-07-2009, 03:28 PM

Visitors found this page by searching for:

underfloor heating mats not heating up

how to shorten underfloor heating mat

electric underfloor heating hot spots

underfloor heating mat not heating up

can you shorten underfloor heating

electric underfloor heating hot patch

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Tilers Forums is the UK's largest wall and floor tiling forum. Advice is provided free of charge to all users. Tilers Forums does not take responsibility for any loss or damage caused due to following advice found on this forum. All wall and floor tiling should be carried out by a qualified wall and floor tiler. Views expressed on this forum are of the users and not Tilers Forums. Views expressed on this tiling forum are of the contributor only and not the forum as a whole. Not all views should be taken as fact but simply the opinion of the person posting. Readers are reminded to seek professional advice before undertaking any wall and floor tiling project.

Tilers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.
DMCA.com
[Output: 127.29 Kb. compressed to 114.66 Kb. by saving 12.63 Kb. (9.92%)]

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28