Discuss UFH sensor question in the Tiling Forum at TilersForums; In the UFH guide it says to run the sensor in conduit so that it can be replaced. I can see the sense in that so I've done that but ...
          
  1. #1
    New TilersForums Contributor jashton's Avatar
    Join Date
    Apr 2010
    Posts
    12
    Thanks
    0
    Thanked 2 Times in 1 Post

    Default UFH sensor question

    In the UFH guide it says to run the sensor in conduit so that it can be replaced. I can see the sense in that so I've done that but am now wondering what to do when I tile. Surely the sensor needs to be bedded in adhesive, just under the tiles so that it picks up a correct temperature? When I laid my SLC I shuttered off a small area around the sensor other wise it would have been bedded in SLC and non-removable.
    So what do I do next. If I don't bed in addy then it will under-read. if I bed in it won't be removable.
    One possible option is to wrap tin foil around the head so it can be bedded in but would then slip out of the foil if I do ever need to replace (unlikely I imagine).
    Any tips/ideas?
    Thx

  2. #2
    Tilers Forums Arms Member
    Yorkshire Tiling Services's Avatar
    Join Date
    Mar 2009
    Location
    Halifax
    Posts
    552
    Thanks
    120
    Thanked 181 Times in 113
    Posts

    Default Re: UFH sensor question

    The conduit should be put in a channel in the floor and self levelled over. The sensor can be inserted afterwards.
    Conduit, if not supplied with kit,can be bought in 2.5 metre lengths, it is usually 10mm in diameter.
    It is designed for use with under floor heating
    Attached Images Attached Images
    Last edited by Yorkshire Tiling Services; 24-07-2010 at 11:10 AM.

  3. The Following User Says Thank You to Yorkshire Tiling Services For This Useful Post:

    jay (24-07-2010)

  4. #3
    jay
    jay is offline
    TilersForums Trusted Member

    jay's Avatar
    Join Date
    Apr 2009
    Location
    Tasmania
    Posts
    8,022
    Thanks
    3,968
    Thanked 1,990 Times in 1,587
    Posts

    Default Re: UFH sensor question

    just to add to the above quote condute should be sealed at one end to stop slc entering and probe must not come in contact with any metal objects ( tin foil included) hope this helps

  5. The Following User Says Thank You to jay For This Useful Post:


  6. #4
    Tilers Forums Arms Member
    Yorkshire Tiling Services's Avatar
    Join Date
    Mar 2009
    Location
    Halifax
    Posts
    552
    Thanks
    120
    Thanked 181 Times in 113
    Posts

    Default Re: UFH sensor question

    Quote Originally Posted by jay View Post
    just to add to the above quote condute should be sealed at one end to stop slc entering and probe must not come in contact with any metal objects ( tin foil included) hope this helps

    Sorry,forgot to mention that

  7. #5
    TilersForums Trusted Member


    Phil Hobson's Avatar
    Join Date
    Aug 2009
    Location
    oldham
    Posts
    7,225
    Thanks
    5,128
    Thanked 3,115 Times in 1,925
    Posts

    Default Re: UFH sensor question

    Spot on advise above, chase in conduit seal end. Slc over, I would add, I usually stretch conduit by placing sealed end under a weight eg. breeze block or the like, then feed in the sensor prior to installing

  8. #6
    New TilersForums Contributor jashton's Avatar
    Join Date
    Apr 2010
    Posts
    12
    Thanks
    0
    Thanked 2 Times in 1 Post

    Default Re: UFH sensor question

    ok so that means the sensor just sits inside the conduit and that the heat will transfer through to give an accurate reading. In that case I just need to pull the sensor back an inch so it's inside the conduit and then seal the end. Easy

    Thanks

  9. #7
    Tilers Forums Arms Member
    diamondtiling's Avatar
    Join Date
    Jun 2009
    Location
    cheshire
    Posts
    6,859
    Thanks
    4,735
    Thanked 3,022 Times in 1,991
    Posts

    Default Re: UFH sensor question

    Quote Originally Posted by jashton View Post
    ok so that means the sensor just sits inside the conduit and that the heat will transfer through to give an accurate reading. In that case I just need to pull the sensor back an inch so it's inside the conduit and then seal the end. Easy

    Thanks
    Yup............

  10. #8
    www.tilernewcastle.co.uk


    timeless john's Avatar
    Join Date
    Feb 2009
    Location
    North East England
    Posts
    6,412
    Thanks
    3,288
    Thanked 3,374 Times in 2,120
    Posts

    Default Re: UFH sensor question

    I always tape the wire at the thermostat end so its not pulled back during connection and moved out of the heating mat area!

    find us : www.tilernewcastle.co.uk visit us : www.timelesstilingsolutions.com

    ' CREATING TIMELESS WALLS & FLOORS - CREATING TIMELESS WALLS & FLOORS '

  11. The Following 2 Users Say Thank You to timeless john For This Useful Post:

    Phil Hobson (24-07-2010)

  12. #9
    TilersForums Trusted Member


    Phil Hobson's Avatar
    Join Date
    Aug 2009
    Location
    oldham
    Posts
    7,225
    Thanks
    5,128
    Thanked 3,115 Times in 1,925
    Posts

    Default Re: UFH sensor question

    Uncanny that TJ, I do exactly that. Great minds and all that

  13. The Following User Says Thank You to Phil Hobson For This Useful Post:

    timeless john (27-07-2010)

  14. #10
    doug boardley
    Guest doug boardley's Avatar

    Default Re: UFH sensor question

    good idea TJ Will do that myself in future

  15. The Following User Says Thank You to doug boardley For This Useful Post:

    timeless john (27-07-2010)

  16. #11
    Established Tiler
    trevortine's Avatar
    Join Date
    Sep 2006
    Location
    East Kilbride
    Posts
    616
    Thanks
    166
    Thanked 192 Times in 107
    Posts

    Default Re: UFH sensor question

    This is a preferred method of mine also but when i challenged the warm up rep about why they dont supply conduit i was informed that they insist on the probe being covered in screed or adhesive to ensure correct readings. It does make sense but would obviously mean lifting a tile to replace if faulty. After many years of fitting them ive never had to change a probe so maybe they have a point? I always tend to fit probe at easy location to change just incase though.

  17. #12
    TilersForums Trusted Member

    kilty55's Avatar
    Join Date
    Apr 2008
    Location
    edinburgh
    Posts
    7,136
    Thanks
    1,488
    Thanked 1,872 Times in 1,492
    Posts

    Default Re: UFH sensor question

    warmups data sheets reccomend conduit but when i called them about this they said the opposite also and said they guarantee the mats etc regardless of conduit being used,

  18. #13
    www.tilernewcastle.co.uk


    timeless john's Avatar
    Join Date
    Feb 2009
    Location
    North East England
    Posts
    6,412
    Thanks
    3,288
    Thanked 3,374 Times in 2,120
    Posts

    Default Re: UFH sensor question

    Quote Originally Posted by doug boardley View Post
    good idea TJ Will do that myself in future
    Had a floor at Christmas that was warm but the thermostat was reading 12 degrees!
    First time 'we' (little john) didn't tape the thermostat end cable and yes the electrician had pulled the cable tight and moved it 30cm out of position.
    So you learn the hard way and it meant taking up 2 tiles to pull it back, but if you mark the location of the sensor on a plan in the guarantee book it makes life easier!
    From what I understand from the electric UFH we have done - mats have a 10 year guarantee and the sensor 2 years - so that should give you all the reasons you need to make it as easy as possible to replace.

    find us : www.tilernewcastle.co.uk visit us : www.timelesstilingsolutions.com

    ' CREATING TIMELESS WALLS & FLOORS - CREATING TIMELESS WALLS & FLOORS '

  19. #14
    Tilers Forums Arms Member lcjohno's Avatar
    Join Date
    Jan 2009
    Location
    Preston
    Posts
    353
    Thanks
    330
    Thanked 110 Times in 62
    Posts

    Default Re: UFH sensor question

    i dont think the manufature garantees the probe for the same time as the heat mats/wire. Thats why i think it needs to be removable. there must be a chance it can fail. If its buried in addy there's a chance you can break all the wires aswell.
    www.precision-tiling.com Tiler in Preston

  20. #15
    Established Tiler
    trevortine's Avatar
    Join Date
    Sep 2006
    Location
    East Kilbride
    Posts
    616
    Thanks
    166
    Thanked 192 Times in 107
    Posts

    Default Re: UFH sensor question

    Quote Originally Posted by lcjohno View Post
    i dont think the manufature garantees the probe for the same time as the heat mats/wire. Thats why i think it needs to be removable. there must be a chance it can fail. If its buried in addy there's a chance you can break all the wires aswell.
    I always screed ufh and have never damaged a mat or probe during installation. You really need to be doing something wrong to do so. Anything can fail but if you install exactly as manufacters instructions then you are covering your back.

  21. #16
    New TilersForums Contributor jashton's Avatar
    Join Date
    Apr 2010
    Posts
    12
    Thanks
    0
    Thanked 2 Times in 1 Post

    Default Re: UFH sensor question

    Well, it's been covered over and inside the conduit for a week now and seems to be accurately measuring temperature. proof will come when I fire up the mat in a couple of weeks

  22. The Following 2 Users Say Thank You to jashton For This Useful Post:

    jay (28-07-2010), timeless john (27-07-2010)

  23. #17
    doug boardley
    Guest doug boardley's Avatar

    Default Re: UFH sensor question

    I had a sensor problem last year.....I forgot to put the beggar in

  24. #18
    Tilers Forums Arms Member lcjohno's Avatar
    Join Date
    Jan 2009
    Location
    Preston
    Posts
    353
    Thanks
    330
    Thanked 110 Times in 62
    Posts

    Default Re: UFH sensor question

    I always screed ufh and have never damaged a mat or probe during installation. You really need to be doing something wrong to do so. Anything can fail but if you install exactly as manufacters instructions then you are covering your back
    I was on about the probe being able to be removed after everything is finished, eg- a year down the line.
    www.precision-tiling.com Tiler in Preston

Similar Threads

  1. need advise on ufh first ufh job.
    By terry the tiler in forum Electric Underfloor Heating
    Replies: 9
    Last Post: 15-04-2010, 05:01 PM
  2. UFH for a new build Orangery ?
    By Lil Dee in forum Electric Underfloor Heating
    Replies: 7
    Last Post: 15-08-2009, 09:52 AM
  3. electric UFH and insulation question
    By Mark B in forum Electric Underfloor Heating
    Replies: 9
    Last Post: 19-04-2009, 08:54 AM
  4. Electric UFH vs Wet UFH - My Verdict
    By ralsmith1 in forum Electric Underfloor Heating
    Replies: 9
    Last Post: 18-04-2009, 04:23 PM
  5. First UFH Job
    By tay1974 in forum Electric Underfloor Heating
    Replies: 2
    Last Post: 19-03-2009, 10:32 AM

Visitors found this page by searching for:

ufh sensor controller location

site:tilersforums.co.uk replacement sensor for warm up underfloor heating

electric ufh sensor

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Tilers Forums is the UK's largest wall and floor tiling forum. Advice is provided free of charge to all users. Tilers Forums does not take responsibility for any loss or damage caused due to following advice found on this forum. All wall and floor tiling should be carried out by a qualified wall and floor tiler. Views expressed on this forum are of the users and not Tilers Forums. Views expressed on this tiling forum are of the contributor only and not the forum as a whole. Not all views should be taken as fact but simply the opinion of the person posting. Readers are reminded to seek professional advice before undertaking any wall and floor tiling project.

Tilers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.
DMCA.com
[Output: 146.90 Kb. compressed to 130.65 Kb. by saving 16.25 Kb. (11.06%)]

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28