Discuss Tiling to Anhydrite screeds... A method statement from PCI. in the Tiling Forum at TilersForums; Here are some guidelines that PCI have allowed me to type up for all you PCI users who need a method statement for tiling to anhydrite screeds... Tiling to Anhydrite ...
          
  1. #1
    Administrator


    Dave's Avatar
    Join Date
    May 2007
    Location
    County Durham
    Posts
    54,472
    Thanks
    9,718
    Thanked 14,141 Times in 9,988
    Posts
    Blog Entries
    1

    Default Tiling to Anhydrite screeds... A method statement from PCI.

    Here are some guidelines that PCI have allowed me to type up for all you PCI users who need a method statement for tiling to anhydrite screeds...


    Tiling to Anhydrite screeds by PCI.



    Anhydrite screeds are now becoming more and more apparent in the market place,and as direct result of this PCI construction systems are being asked to specify products for this type of finish.

    The following is issued as a guidline :

    It is important that the screed has been laid as per the latest manufacturer's data sheet,paying particular attention to:

    1. Underfloor heating
    2. Residual moisture conten
    3. Flor finishes-surface preperation.



    1.
    Anhydrite screeds are suited for underfloor heating since they are laid much thinner than traditional screeds, and therefore eliminate air pockets and voids around heating pipes etc....

    In heated calcium sulphate floors,movement joints should be carried through both the screed and the tile bed dividing the tiling into area's no greater then 40m2, or in accordance with the sceed manufacturers instructions....
    The area bounded by the movement joints should be square to rectangular with the width to length ratio not exceeding 5 to 8 mtrs.....

    2.
    Residual moisture content of 0.5% or less must be obtained before the application of primer G, drying times of the screed is normally approximatley 1mm per day uoto 40mm and 0.5mm per day thereafter at 20c,65-70 relative humidity.
    To reach this figure of 0.5% witht he use of underfloor heating, it should be borne in mind that this will increase the humidity of the site.

    It is therefore essential that good ventilation be maintained during this period of drying.

    3.
    If underfloor heating is being used- turn off 48 hrs prior to the following applications..and commissioning of the heating.

    Ensure that the surface of the screed is free of any dirt,dust,oil,grease or any other contamination likely to prevent a good bonding surface.
    The finished surface should be abraded/sanded then cleaned with a vacuum cleaner if laitence is present.

    Apply primer G, diluted 1:1 with water to the whole area, ensuring a continous coat of the primer without the formation of puddles.

    When dry a second coat must be applied NEAT as above.

    Primer G is coloured blue to facilitate this application.
    When the primer is dry then tiling can be carried out with the appropiate PCI adhesive to suit .

    If underfloor heating is integrated in the system th en this must be left off for a further 48 hrs after completion of the grouting and then gradually increase the heat over the next 7 days.
    This will reduce the possibility of any thermal shock being appied to the over all system..

  2. The Following 6 Users Say Thank You to Dave For This Useful Post:

    Dan (15-02-2010), deanotile (12-02-2010), diamondtiling (13-02-2010), pete f (12-02-2010), TF Ed (12-02-2010)

  3. #2
    Healthy TilersForums Contributor penkhull's Avatar
    Join Date
    Feb 2010
    Posts
    110
    Thanks
    0
    Thanked 15 Times in 15
    Posts

    Default Re: Tiling to Anhydrite screeds... A method statement from PCI.

    I've heard a new way of doing this. If you use an uncoupling system you can complete the floor with out removing the finer particles on the surface and without priming. The whole point of an uncoupling membrane is that it doesn't stick to the floor.

    It was confirmed that this would work by Lafarge although they would still prefer you to prime the floor they admitted there was no need.

  4. #3
    TF Moderator & Pro Tiler


    whitebeam's Avatar
    Join Date
    Apr 2007
    Location
    Hertfordshire
    Posts
    22,960
    Thanks
    2,314
    Thanked 4,999 Times in 4,312
    Posts

    Default Re: Tiling to Anhydrite screeds... A method statement from PCI.

    Do you mean just lay the uncoupling direct onto the floor without any adhesive
    "Experience is simply the name we give our mistakes"

  5. #4
    Healthy TilersForums Contributor penkhull's Avatar
    Join Date
    Feb 2010
    Posts
    110
    Thanks
    0
    Thanked 15 Times in 15
    Posts

    Default Re: Tiling to Anhydrite screeds... A method statement from PCI.

    No you need to stick it down to hold it in place but then it doesn't matter if it comes away, it doesn't really matter what you stick it down with.

  6. #5
    TF Moderator & Pro Tiler


    whitebeam's Avatar
    Join Date
    Apr 2007
    Location
    Hertfordshire
    Posts
    22,960
    Thanks
    2,314
    Thanked 4,999 Times in 4,312
    Posts

    Default Re: Tiling to Anhydrite screeds... A method statement from PCI.

    If it comes away it will be cracking all over the place, don't sound good to me IMO
    "Experience is simply the name we give our mistakes"

  7. #6
    TilersForums Trusted Member


    Phil Hobson's Avatar
    Join Date
    Aug 2009
    Location
    oldham
    Posts
    7,225
    Thanks
    5,128
    Thanked 3,115 Times in 1,925
    Posts

    Default Re: Tiling to Anhydrite screeds... A method statement from PCI.

    Quote Originally Posted by penkhull View Post
    I've heard a new way of doing this. If you use an uncoupling system you can complete the floor with out removing the finer particles on the surface and without priming. The whole point of an uncoupling membrane is that it doesn't stick to the floor.

    It was confirmed that this would work by Lafarge although they would still prefer you to prime the floor they admitted there was no need.

    Sorry I must be thinking of a different decoupling membrane, I use Ditra or Dural CI. Both of which Need the fleece to be securely fixed to the substrate. Otherwise you might as well lay cling film, and save a lot of money

  8. #7
    Administrator


    Dave's Avatar
    Join Date
    May 2007
    Location
    County Durham
    Posts
    54,472
    Thanks
    9,718
    Thanked 14,141 Times in 9,988
    Posts
    Blog Entries
    1

    Default Re: Tiling to Anhydrite screeds... A method statement from PCI.

    Quote Originally Posted by penkhull View Post
    No you need to stick it down to hold it in place but then it doesn't matter if it comes away, it doesn't really matter what you stick it down with.

    In theory you still use the required adhesive for the job... but if it does uncouple then the membrane will cope.. as there is no deflection then it just sits on the surface...

    You can actually get another brand of uncoupling membrane that doesn't stick down, it just lays loose and locks together at the edges so it doesn't move as you tile..

    So to answer your theory above.. then guy from lafarge is correct in a sort of way.

    But my post is what a PCI user need to do, to use PCI adhesives.. uncouplers is another thread.

  9. #8
    Tilers Forums Pro - Screed Advisor
    Ajax123's Avatar
    Join Date
    Apr 2009
    Location
    Lincolnshire
    Posts
    3,015
    Thanks
    329
    Thanked 1,513 Times in 926
    Posts
    Blog Entries
    1

    Default Re: Tiling to Anhydrite screeds... A method statement from PCI.

    Quote Originally Posted by penkhull View Post
    I've heard a new way of doing this. If you use an uncoupling system you can complete the floor with out removing the finer particles on the surface and without priming. The whole point of an uncoupling membrane is that it doesn't stick to the floor.

    It was confirmed that this would work by Lafarge although they would still prefer you to prime the floor they admitted there was no need.

    Who at Lafarge confirmed this Penkhull
    you must all buy this song from any good download site for just 79p. Proceeds to Blesma, RAFA and RAFBF charities



    Teresa Hind - The Fight Goes On

  10. #9
    Tilers Forums Pro - Screed Advisor
    Ajax123's Avatar
    Join Date
    Apr 2009
    Location
    Lincolnshire
    Posts
    3,015
    Thanks
    329
    Thanked 1,513 Times in 926
    Posts
    Blog Entries
    1

    Default Re: Tiling to Anhydrite screeds... A method statement from PCI.

    Quote Originally Posted by Dave View Post
    In theory you still use the required adhesive for the job... but if it does uncouple then the membrane will cope.. as there is no deflection then it just sits on the surface...

    You can actually get another brand of uncoupling membrane that doesn't stick down, it just lays loose and locks together at the edges so it doesn't move as you tile..

    So to answer your theory above.. then Alan from lafarge is correct.

    But my post is what a PCI user need to do, to use PCI adhesives.. uncouplers is another thread.
    Not guilty (I don't think) although I agree that the uncoupling membrane should at least be nominally adhered to prevent rucking and horizontal movement.

    Back to the thread though. I am not familiar with primer G although I know it is an acrylic. The first coat being diluted is good practice as this encourages the primer to penetrate into the surface. However you need to be a little carefull in the application as you are "adding" water to the screed which will need time to dry out - I owuld think 24 hours.

    I still prefer to see Epoxy Primers with cement based adhesives. whilst water dispersed the way epoxy cures it uses a good proportion of the water in the curing process. Epoxys are also much better at preventing the migration of sulphates so are much more robust against the dreaded ettringite reaction. Of course Gyspum adhesive is even better still at preventing this reaction. I think PCI do a gypsum adhesive in Germany - they certainly do a gypsum leveller.

    Other than that PCI seem to have it pretty correct.
    you must all buy this song from any good download site for just 79p. Proceeds to Blesma, RAFA and RAFBF charities



    Teresa Hind - The Fight Goes On

  11. #10
    Tilers Forums Arms Member

    peckers's Avatar
    Join Date
    Jun 2009
    Location
    I live on the Devon/Cornwall border line
    Posts
    1,479
    Thanks
    788
    Thanked 904 Times in 508
    Posts

    Default Re: Tiling to Anhydrite screeds... A method statement from PCI.

    Quote Originally Posted by Ajax123 View Post
    Not guilty (I don't think) although I agree that the uncoupling membrane should at least be nominally adhered to prevent rucking and horizontal movement.

    Back to the thread though. I am not familiar with primer G although I know it is an acrylic. The first coat being diluted is good practice as this encourages the primer to penetrate into the surface. However you need to be a little carefull in the application as you are "adding" water to the screed which will need time to dry out - I owuld think 24 hours.

    I still prefer to see Epoxy Primers with cement based adhesives. whilst water dispersed the way epoxy cures it uses a good proportion of the water in the curing process. Epoxys are also much better at preventing the migration of sulphates so are much more robust against the dreaded ettringite reaction. Of course Gyspum adhesive is even better still at preventing this reaction. I think PCI do a gypsum adhesive in Germany - they certainly do a gypsum leveller.

    Other than that PCI seem to have it pretty correct.
    What make of epoxy sealers would you recommend for anhydrated floors and cement based adhesives?
    Creative tiling
    With a personal touch!
    www.stevepecktiling.co.uk

  12. #11
    Administrator


    Dave's Avatar
    Join Date
    May 2007
    Location
    County Durham
    Posts
    54,472
    Thanks
    9,718
    Thanked 14,141 Times in 9,988
    Posts
    Blog Entries
    1

    Default Re: Tiling to Anhydrite screeds... A method statement from PCI.

    Quote Originally Posted by Ajax123 View Post
    Not guilty (I don't think) although I agree that the uncoupling membrane should at least be nominally adhered to prevent rucking and horizontal movement.

    Back to the thread though. I am not familiar with primer G although I know it is an acrylic. The first coat being diluted is good practice as this encourages the primer to penetrate into the surface. However you need to be a little carefull in the application as you are "adding" water to the screed which will need time to dry out - I owuld think 24 hours.

    I still prefer to see Epoxy Primers with cement based adhesives. whilst water dispersed the way epoxy cures it uses a good proportion of the water in the curing process. Epoxys are also much better at preventing the migration of sulphates so are much more robust against the dreaded ettringite reaction. Of course Gyspum adhesive is even better still at preventing this reaction. I think PCI do a gypsum adhesive in Germany - they certainly do a gypsum leveller.

    Other than that PCI seem to have it pretty correct.
    That is just the same as using adhesive Alan.. it will get wet.... but as mentioned above.. it does say to leave to dry..between coats.

  13. #12
    Healthy TilersForums Contributor penkhull's Avatar
    Join Date
    Feb 2010
    Posts
    110
    Thanks
    0
    Thanked 15 Times in 15
    Posts

    Default Re: Tiling to Anhydrite screeds... A method statement from PCI.

    Who ever the technical guy is who covers Derby. If you think about it it makes sense if you stick the uncoupling membrane down with a rapid SPF it will defo hold in place whilst you tile it and then if it uncouples after you have tiled it the membrane is doing its job.

    I do think if you're going to do it by a more conventional method then an epoxy primer is better once you've removed the smaller particles that come to the surface, at least then you know you've got it covered, with an acyrlic type primer you have to keep soaking it in until its saturated.

  14. #13
    Tilers Forums Pro - Screed Advisor
    Ajax123's Avatar
    Join Date
    Apr 2009
    Location
    Lincolnshire
    Posts
    3,015
    Thanks
    329
    Thanked 1,513 Times in 926
    Posts
    Blog Entries
    1

    Default Re: Tiling to Anhydrite screeds... A method statement from PCI.

    Quote Originally Posted by peckers View Post
    What make of epoxy sealers would you recommend for anhydrated floors and cement based adhesives?
    Tremco CS Epoxy (2 coats neat) or Laybond Screedmaster Epoxy (dilute 1:1 with clean water - 1 coat usually sufficient but 2 to be certain) are the ones I usually point people towards. They also serve to make the surface much harder and more stable.
    you must all buy this song from any good download site for just 79p. Proceeds to Blesma, RAFA and RAFBF charities



    Teresa Hind - The Fight Goes On

  15. The Following User Says Thank You to Ajax123 For This Useful Post:

    peckers (13-02-2010)

Similar Threads

  1. Replies: 10
    Last Post: 06-07-2008, 10:39 AM
  2. Anhydrite Screeds - Increase In Tiling Queries
    By Dave in forum Tiling Forum
    Replies: 1
    Last Post: 05-11-2007, 08:57 PM
  3. Tiling NVQ
    By Dan in forum Tiling NVQ's
    Replies: 1
    Last Post: 09-05-2007, 11:45 PM
  4. Tiling Courses & Tiling Course Companies
    By Dan in forum Tiling Courses Feedback
    Replies: 0
    Last Post: 02-04-2006, 10:49 PM

Visitors found this page by searching for:

spf adhesive anhydrite screed

screed anhydrite germany

germany anhydrite screed

ceramic tiler method statement

laybond screedmaster epoxy

anhydrite screed germany

method of statement for screed

pci gypsum adhesive

guidelines for tiling screeds

pci adhesie for anhydrite screeds

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Tilers Forums is the UK's largest wall and floor tiling forum. Advice is provided free of charge to all users. Tilers Forums does not take responsibility for any loss or damage caused due to following advice found on this forum. All wall and floor tiling should be carried out by a qualified wall and floor tiler. Views expressed on this forum are of the users and not Tilers Forums. Views expressed on this tiling forum are of the contributor only and not the forum as a whole. Not all views should be taken as fact but simply the opinion of the person posting. Readers are reminded to seek professional advice before undertaking any wall and floor tiling project.

Tilers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.
DMCA.com
[Output: 139.06 Kb. compressed to 126.14 Kb. by saving 12.92 Kb. (9.29%)]

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28