Discuss Reducing Soil Pipe in the Tiling Forum at TilersForums; hi everyone, is it possible to reduce the diameter of the soil pipe from the toilet to the stack. Just found out the house has an internal stack and the ...
          
  1. #1
    Tilers Forums Arms Member janzbro's Avatar
    Join Date
    May 2009
    Location
    Teesside
    Posts
    81
    Thanks
    26
    Thanked 4 Times in 3
    Posts

    Default Reducing Soil Pipe

    hi everyone, is it possible to reduce the diameter of the soil pipe from the toilet to the stack.

    Just found out the house has an internal stack and the toilet waste goes through the wall into the airing cupboard and then drops down stairs.
    This is leaving me with limited space across the back wall to fit a 1200 x 900 shower tray and fit a stud wall boxing in the soil pipe and the shower hot/cold supplies as I only have 1325mm wall to wall.

    I could put a stud under the soil pipe and build a stud frame above it then board the wall, this would leave the p/board touching the soil pipe but Im worried about movement of that upper frame.

    Any ideas on framing out or reducing the soil pipe would be much appreciated.
    If It Can Go Wrong, It Probably Will !!!!

  2. #2
    Regular TilersForums Contributor

    365drills's Avatar
    Join Date
    May 2007
    Location
    Live in London
    Posts
    2,514
    Thanks
    315
    Thanked 869 Times in 544
    Posts

    Default Re: Reducing Soil Pipe

    Probably need more info!


    When I first read post this is what I assumed you were asking. To reduce the stack.

    But I think you want to box in a soil stack with the minimum of plasterboard. Is that right?



    I boxed in the whole back wall then jammed the loo up against the tiles.

    But I think you are saying you need to sacrifice space for a shower. Assuming the soil stack is fixed (cant be altered) then all you can do is work with the space you have. It may mean a 1000mm tray.
    Richard Hazell - Diamond Tile Drills
    Decent reliable gear that wont let you down
    01992-410636 0777 366 4519
    richard@365drills.com
    http://www.365drills.com
    Tile Drills

  3. #3
    Tilers Forums Arms Member

    tommyzooom's Avatar
    Join Date
    Sep 2008
    Location
    Ireland
    Posts
    1,226
    Thanks
    699
    Thanked 739 Times in 353
    Posts

    Default Re: Reducing Soil Pipe

    Do you want to box in the pipe in a corner, If so WEDI do a preformed corner for this purpose, will save you some room

  4. #4
    Tilers Forums Arms Member janzbro's Avatar
    Join Date
    May 2009
    Location
    Teesside
    Posts
    81
    Thanks
    26
    Thanked 4 Times in 3
    Posts

    Default Re: Reducing Soil Pipe

    sorry it was as clear as mud wasnt it

    The main aim as you point out is to get the 1200 x 900 tray in

    I was thinking if I could reduce the soil pipe diameter (only for approx 900mm where it runs between the tray and the wall at one end , that this would allow me to get some studs in from floor to ceiling and board it out (so hiding the waste and shower supplies).
    If It Can Go Wrong, It Probably Will !!!!

  5. #5
    Regular TilersForums Contributor simhopper's Avatar
    Join Date
    Feb 2008
    Posts
    269
    Thanks
    1
    Thanked 97 Times in 68
    Posts

    Default Re: Reducing Soil Pipe

    From a plumber, you can not reduce the bore size of the soil pipe

    Anything above the toilet wc connection level, as long as it is a vent only could be reduced to 3", if the stack continues to feed upper floors/flats then it must remain 4"

    You have 135mm, which if the frame is done correctly should allow enough space, if you are worried about the framework touching it why not chisel away any plaster and fit he soilpipe snug against the brickwork

  6. #6
    Tilers Forums Arms Member janzbro's Avatar
    Join Date
    May 2009
    Location
    Teesside
    Posts
    81
    Thanks
    26
    Thanked 4 Times in 3
    Posts

    Default Re: Reducing Soil Pipe

    not worried about the stud work touching it is just gettting the stud work solid, as it the wall the shower / mixer will be on and be fully tiled inside a cubicle and dont want the water getting in a the tiles falling off

    dont suppose you could explain how to do it or sent me a pic

    Ive got 135mm left

    Soil pipe = 105mm
    Stud frame 4"x2" = 105mm x 52.5mm
    P/board = 12.5mm

    Im not sure how you would do it because at the least with the stud side on it would take up 170mm - well over what I have
    Last edited by janzbro; 10-05-2009 at 04:31 PM.
    If It Can Go Wrong, It Probably Will !!!!

  7. #7
    Regular TilersForums Contributor simhopper's Avatar
    Join Date
    Feb 2008
    Posts
    269
    Thanks
    1
    Thanked 97 Times in 68
    Posts

    Default Re: Reducing Soil Pipe

    Quote Originally Posted by janzbro View Post
    not worried about the stud work touching it is just gettting the stud work solid, as it the wall the shower / mixer will be on and be fully tiled inside a cubicle and dont want the water getting in a the tiles falling off

    dont suppose you could explain how to do it or sent me a pic

    Ive got 135mm left

    Soil pipe = 105mm
    Stud frame 4"x2" = 105mm x 52.5mm
    P/board = 12.5mm

    Im not sure how you would do it because at the least with the stud side on it would take up 170mm - well over what I have
    You want to do something like this



    This job was 4by2 timber bolted to the wall with hammer fixings, we did 4 horizontal timbers, We then screwed vertical 4 by 2 with plastic shim washers to level out.As you can see the soilpipe is free to be fitted at the bottom

  8. The Following 4 Users Say Thank You to simhopper For This Useful Post:

    365drills (10-05-2009), faithhealer (10-05-2009), Gazebo (11-05-2009), janzbro (10-05-2009)

  9. #8
    Tilers Forums Arms Member janzbro's Avatar
    Join Date
    May 2009
    Location
    Teesside
    Posts
    81
    Thanks
    26
    Thanked 4 Times in 3
    Posts

    Default Re: Reducing Soil Pipe

    never thought of that, your a star

    simple when you know how or see a photo

    cheers you just saved me rethinking the whole project
    If It Can Go Wrong, It Probably Will !!!!

  10. #9
    Tilers Forums Arms Member Swanseajack's Avatar
    Join Date
    May 2008
    Location
    Swansea
    Posts
    48
    Thanks
    49
    Thanked 15 Times in 9
    Posts

    Default Re: Reducing Soil Pipe

    Also, could use 3x2 CLS for stud work instead of 4x2? Another option maybe to use a Durgo Valve, depending on stack layout.
    Last edited by Swanseajack; 10-05-2009 at 06:55 PM.

  11. #10
    Regular TilersForums Contributor simhopper's Avatar
    Join Date
    Feb 2008
    Posts
    269
    Thanks
    1
    Thanked 97 Times in 68
    Posts

    Default Re: Reducing Soil Pipe

    Quote Originally Posted by Swanseajack View Post
    Also, could use 3x2 CLS for stud work instead of 4x2? Another option maybe to use a Durgo Valve, depending on stack layout.
    You can not always use a durgo

    All houses must have at least one vent to atmosphere, if his property is a one stack house then he must not use a durgo

  12. #11
    Regular TilersForums Contributor bighen's Avatar
    Join Date
    Oct 2007
    Location
    Eastwood, Nottingham
    Posts
    380
    Thanks
    11
    Thanked 41 Times in 38
    Posts

    Default Re: Reducing Soil Pipe

    Quote Originally Posted by simhopper View Post
    You can not always use a durgo

    All houses must have at least one vent to atmosphere, if his property is a one stack house then he must not use a durgo

    Not quite true.

    You work on a 1 in 3 principle. ie. every 3rd house must vent to atmosphere. the other 2 can utilize air admittance valves.

    Knew my years in management would come in useful eventually

  13. #12
    Regular TilersForums Contributor simhopper's Avatar
    Join Date
    Feb 2008
    Posts
    269
    Thanks
    1
    Thanked 97 Times in 68
    Posts

    Default Re: Reducing Soil Pipe

    Quote Originally Posted by bighen View Post
    Not quite true.

    You work on a 1 in 3 principle. ie. every 3rd house must vent to atmosphere. the other 2 can utilize air admittance valves.

    Knew my years in management would come in useful eventually
    Different councils, different rules

    When i have dealt with Edinburgh building control they have insisted on this

    I would always prefer to vent to atmos, We had issues in a large developent of new flats where the durgos had been badly fitted, it was only when we tested that we found out the valves where not correctly seated

  14. #13
    Regular TilersForums Contributor bighen's Avatar
    Join Date
    Oct 2007
    Location
    Eastwood, Nottingham
    Posts
    380
    Thanks
    11
    Thanked 41 Times in 38
    Posts

    Default Re: Reducing Soil Pipe

    Scotland has a totally different set of rules to England.

    Roof bracing/covering technique due to stronger winds
    Plaster thickness - 5mm min
    etc

    But the NHBC stipulate the 1 in 3 rule to which all the councils in England I have dealt with accept

  15. #14
    Tilers Forums Arms Member Gazebo's Avatar
    Join Date
    Aug 2008
    Location
    Brighton
    Posts
    659
    Thanks
    290
    Thanked 108 Times in 94
    Posts

    Default Re: Reducing Soil Pipe

    I am with bighen on this one. 1 in 3 vent to atmosphere, i only use AAV (dergo) when i have moved a w/c or extended the branch run into the SVP beyond 1.5m of the vent pipe.

    I think that is the regulation.correct me if i am rusty on that reg.

  16. #15
    Tilers Forums Arms Member janzbro's Avatar
    Join Date
    May 2009
    Location
    Teesside
    Posts
    81
    Thanks
    26
    Thanked 4 Times in 3
    Posts

    Default Re: Reducing Soil Pipe

    Im only moving the toilet location from 1m away from the stack on one wall to 1.5m away on another wall not going to be altering any vents just the soil pipe route

    but concerning the stud work,

    should I remove the old dot and dab plasterboard before attaching the stad or can/should I just stud over it ?
    Last edited by janzbro; 11-05-2009 at 11:48 AM.
    If It Can Go Wrong, It Probably Will !!!!

  17. #16
    Regular TilersForums Contributor

    365drills's Avatar
    Join Date
    May 2007
    Location
    Live in London
    Posts
    2,514
    Thanks
    315
    Thanked 869 Times in 544
    Posts

    Default Re: Reducing Soil Pipe


    If it were me I would start from scratch.


    Thats what I did when I rebuilt the studwork and changed the soil stack for this loo.



    The soil stack was laid out first.
    The stud wall was rebuilt to conceal it.
    To reclaim lost space, niches were cut into the wall above the soil stack for storage.
    The whole area was neatly tiles to conceal all pipework.
    Richard Hazell - Diamond Tile Drills
    Decent reliable gear that wont let you down
    01992-410636 0777 366 4519
    richard@365drills.com
    http://www.365drills.com
    Tile Drills

Similar Threads

  1. pipe detectors
    By fad in forum Tiling Tools
    Replies: 6
    Last Post: 25-04-2009, 01:38 PM
  2. hot water pipe cracking tiles
    By kilty55 in forum Tiling Forum
    Replies: 13
    Last Post: 20-08-2008, 07:37 PM
  3. Replies: 0
    Last Post: 26-03-2008, 04:00 PM
  4. DISASTER - Hit a water pipe & gas pipe with nails
    By tysfoot in forum Tiling Forum
    Replies: 48
    Last Post: 30-11-2007, 07:32 PM

Visitors found this page by searching for:

soil pipe sizes

soil pipe vent diameter

durgo valves

minimum soil pipe diameter

toilet soil pipe size

images boxed in toilet

building regs boxing internal soil pipe

relocate soil stack

soil stack requirements

pre formed plywood pipe boxing

boxing in toilet soil pipe

soil pipes uk

how to conceal toilet pipes

tiling toilet wall

soil stack connections

internal vented soil pipe

soil pipe in house

soil stack pipes diameter

reduction in diameter of soil ventilation pipe

box in soil pipe

svp dergo

altering toilet soil pipes

soil pipe toilet size

what size pipe can i vent a soil

uk toilet stack pipe

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Tilers Forums is the UK's largest wall and floor tiling forum. Advice is provided free of charge to all users. Tilers Forums does not take responsibility for any loss or damage caused due to following advice found on this forum. All wall and floor tiling should be carried out by a qualified wall and floor tiler. Views expressed on this forum are of the users and not Tilers Forums. Views expressed on this tiling forum are of the contributor only and not the forum as a whole. Not all views should be taken as fact but simply the opinion of the person posting. Readers are reminded to seek professional advice before undertaking any wall and floor tiling project.

Tilers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.
DMCA.com
[Output: 135.67 Kb. compressed to 120.74 Kb. by saving 14.92 Kb. (11.00%)]

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28