Results 1 to 18 of 18
Discuss Do I need an uncoupling layer over new screed? in the Tile Adhesive, Grout and Substrate Preparation at TilersForums; Hi folks, I'm looking for some thoughts on an uncoupling layer - the posts already here have helped a bit but.... We're looking at laying a new kitchen / family ...
          
  1. #1
    giz
    Guest giz's Avatar

    Default Do I need an uncoupling layer over new screed?

    Hi folks,

    I'm looking for some thoughts on an uncoupling layer - the posts already here have helped a bit but....

    We're looking at laying a new kitchen / family area thats about 34sq-m if size matters.

    Here's the detail:
    Slurried Block and beam base over a void.
    125mm Celotex insulation
    Wet UFH in a 50mm rapid set screed.
    PEI 5 grade Porcelain tiles on a flexible adhesive.

    I want to tile within 2 weeks of the screed going down and I'd like to know if I need to use an uncoupling layer such as Schluter DITRA (is there a cheaper equivalent that's as good)?

    Advice and tips gratefully received.
    Thanks

  2. #2
    Administrator


    Dave's Avatar
    Join Date
    May 2007
    Location
    County Durham
    Posts
    54,465
    Thanks
    9,718
    Thanked 14,141 Times in 9,988
    Posts
    Blog Entries
    1

    Default Re: Do I need an uncoupling layer over new screed?

    Hi and welcome..

    Dural Ci.. is one i use and perfect for green screeds... also better than a green screed adhesive as the membrane allows for shrinkage and expansion... it will also cope with none-commissioned floors with UFH as long as you heat then very slowly once ready to turn the UFH on..

  3. The Following 2 Users Say Thank You to Dave For This Useful Post:

    andy-p (09-09-2010), Richard Edwards (09-09-2010)

  4. #3
    Tilers Forums Arms Member simon1's Avatar
    Join Date
    Feb 2010
    Location
    Woking, Surrey
    Posts
    109
    Thanks
    68
    Thanked 25 Times in 22
    Posts

    Default Re: Do I need an uncoupling layer over new screed?

    I would without doubt - Dural Ci is my choice

  5. #4
    pjc
    pjc is offline
    TilersForums Trusted Member

    pjc's Avatar
    Join Date
    Oct 2007
    Location
    high wycombe
    Posts
    4,181
    Thanks
    244
    Thanked 688 Times in 537
    Posts

    Default Re: Do I need an uncoupling layer over new screed?

    Dave would he still need green screed adhesive with rapid screed ?

  6. #5
    Administrator


    Dave's Avatar
    Join Date
    May 2007
    Location
    County Durham
    Posts
    54,465
    Thanks
    9,718
    Thanked 14,141 Times in 9,988
    Posts
    Blog Entries
    1

    Default Re: Do I need an uncoupling layer over new screed?

    Will a rapid screed lose moisture quick enough to tile pete.. i know it will hydrate chemically quicker but there is the moisture issue IMO.. also the heat issue if not commissioned and you cannot commission it that soon ..

  7. The Following User Says Thank You to Dave For This Useful Post:

    pjc (09-09-2010)

  8. #6
    pjc
    pjc is offline
    TilersForums Trusted Member

    pjc's Avatar
    Join Date
    Oct 2007
    Location
    high wycombe
    Posts
    4,181
    Thanks
    244
    Thanked 688 Times in 537
    Posts

    Default Re: Do I need an uncoupling layer over new screed?

    thats a good point Dave now what about this fight

  9. #7
    Administrator


    Dave's Avatar
    Join Date
    May 2007
    Location
    County Durham
    Posts
    54,465
    Thanks
    9,718
    Thanked 14,141 Times in 9,988
    Posts
    Blog Entries
    1

    Default Re: Do I need an uncoupling layer over new screed?


  10. #8
    Tilers Forums Arms Member buddha1964's Avatar
    Join Date
    Nov 2009
    Posts
    186
    Thanks
    26
    Thanked 37 Times in 28
    Posts

    Default Re: Do I need an uncoupling layer over new screed?

    Can you use a green screed addy under a decoupling mat on an uncomissioned floor then.

  11. #9
    TilersForums Trusted Member


    Phil Hobson's Avatar
    Join Date
    Aug 2009
    Location
    oldham
    Posts
    7,224
    Thanks
    5,128
    Thanked 3,115 Times in 1,925
    Posts

    Default Re: Do I need an uncoupling layer over new screed?

    Quote Originally Posted by buddha1964 View Post
    Can you use a green screed addy under a decoupling mat on an uncomissioned floor then.
    Good point, I would say yes i have never done it myself but it does make sense. I'm with Dave on the Dural CI

  12. #10
    doug boardley
    Guest doug boardley's Avatar

    Default Re: Do I need an uncoupling layer over new screed?

    Just wondering how long OP should leave UFH before comissioning it now, what do you guys think, 6-7 weeks?

  13. #11
    Tilers Forums Pro - Screed Advisor
    Ajax123's Avatar
    Join Date
    Apr 2009
    Location
    Lincolnshire
    Posts
    3,014
    Thanks
    329
    Thanked 1,513 Times in 926
    Posts
    Blog Entries
    1

    Default Re: Do I need an uncoupling layer over new screed?

    Quote Originally Posted by giz View Post
    Hi folks,

    I'm looking for some thoughts on an uncoupling layer - the posts already here have helped a bit but....

    We're looking at laying a new kitchen / family area thats about 34sq-m if size matters.

    Here's the detail:
    Slurried Block and beam base over a void.
    125mm Celotex insulation
    Wet UFH in a 50mm rapid set screed.
    PEI 5 grade Porcelain tiles on a flexible adhesive.

    I want to tile within 2 weeks of the screed going down and I'd like to know if I need to use an uncoupling layer such as Schluter DITRA (is there a cheaper equivalent that's as good)?

    Advice and tips gratefully received.
    Thanks
    I would say an uncoupling membrane is essential in this one. This is mainly due to the screed not being deep enough to do its job. Sand cement screeds should be laid at a minimum depth of 65mm when floating. This by virtue of it being on Celotex is floating. The thinner the screed is the more propensity it has to curl and the weaker it is in tension so the more it is likely to crack.

    Rapid drying screeds are simply sand cement screeds with an additive which is usually a plasticiser which reduces the water content. To hydrate fully cement needs less water than you might think and a good deal of the water in traditional screeds is there for workability purposes. Typically a rapid drying screed will fry at around 25mm per week however they should be cured first for 7 days following installation. This is more important in these types of screeds because the loss of water when there is already not much ion the period during which the chemical reaction is at its fiercest can lead to drying shrinkage cracking. This may not be immediately visible and often manifests itself more when the heating is commisioned.

    The underfloor heating MUST be comissioned prior to installing any type of covering on any type of deep screed. An uncoupling membrane and a green screed adhesive do NOT replace the need for good practice.

    Regardless of the type of sand cement screed the underfloor heating should not be comissioned for a period of 28 days following installation. this is based on the rate of gain of strength associated with screeds and testing etc. which are carried out and therefore declared at 28 days age. Comissioning sooner than this could exacerbate cracking and will almost certainly lead to cracking especially given the shallow depth. It is not always about moisture I'm afraid.

    Sorry to say but tiling this screed after just 2 weeks is foolhardy and fraught with risk and would force you to operate outside of national standards. Not what you wanted to hear I know but standards are standards.
    you must all buy this song from any good download site for just 79p. Proceeds to Blesma, RAFA and RAFBF charities



    Teresa Hind - The Fight Goes On

  14. The Following 10 Users Say Thank You to Ajax123 For This Useful Post:

    buddha1964 (09-09-2010), diamondtiling (12-06-2011), EH TILING (26-10-2010), jay (12-06-2011), Nardini (10-09-2010), Phil Hobson (09-09-2010), Richard Edwards (09-09-2010), whitebeam (09-09-2010)

  15. #12
    Established Tiler
    Richard Edwards's Avatar
    Join Date
    Mar 2009
    Location
    South Wales
    Posts
    375
    Thanks
    392
    Thanked 261 Times in 131
    Posts

    Default Re: Do I need an uncoupling layer over new screed?

    Hi Ajax

    I'm always interested in your posts and read them front to back and again to digest them in detail

    Are you saying that if a standard screed was used in this case, say 75mm deep or deeper then as long as you left long enough time to fully dry out and commisioned the UFH properly prior to laying tiles, then a quality polymer modified ady - ie one part flex or standard high resin ady with polymer additive would be all that was needed and no need to use uncoupling mem. ?

    I like the advice about good practice - -sound !
    Richard Edwards - The Quality Tiling Co Ltd
    Where excellence comes as standard
    01443 206517 / 0778 626 7395
    www.thequalitytiling.co.uk -

  16. #13
    Administrator


    Dave's Avatar
    Join Date
    May 2007
    Location
    County Durham
    Posts
    54,465
    Thanks
    9,718
    Thanked 14,141 Times in 9,988
    Posts
    Blog Entries
    1

    Default Re: Do I need an uncoupling layer over new screed?

    Too add to above post.. ( Ajax 123)Schluter do say that their membrane can be used on an Un-commissioned screed floor.. The heating needs to be slowly turned up and the membrane will cope with screed shrinkage and expansion.. I got this verbally direct from Schluter technical..

    So we have a few membranes that work in the same way.. so will work for all then,, but expansion joints must be used in respect to BS5385..

  17. #14
    Tilers Forums Pro - Screed Advisor
    Ajax123's Avatar
    Join Date
    Apr 2009
    Location
    Lincolnshire
    Posts
    3,014
    Thanks
    329
    Thanked 1,513 Times in 926
    Posts
    Blog Entries
    1

    Default Re: Do I need an uncoupling layer over new screed?

    Quote Originally Posted by Dave View Post
    Too add to above post.. ( Ajax 123)Schluter do say that their membrane can be used on an Un-commissioned screed floor.. The heating needs to be slowly turned up and the membrane will cope with screed shrinkage and expansion.. I got this verbally direct from Schluter technical..

    So we have a few membranes that work in the same way.. so will work for all then,, but expansion joints must be used in respect to BS5385..

    You are right Dave about Schluter and if the screed was designed and installed correctly I would have fewer concerns. In this case it seems it hasn't. I'd bet my beer that it has no expansion joints in it either.....
    you must all buy this song from any good download site for just 79p. Proceeds to Blesma, RAFA and RAFBF charities



    Teresa Hind - The Fight Goes On

  18. #15
    Administrator


    Dave's Avatar
    Join Date
    May 2007
    Location
    County Durham
    Posts
    54,465
    Thanks
    9,718
    Thanked 14,141 Times in 9,988
    Posts
    Blog Entries
    1

    Default Re: Do I need an uncoupling layer over new screed?

    Probs not... i wonder who spec'd that one Al..

  19. #16
    Tilers Forums Pro - Screed Advisor
    Ajax123's Avatar
    Join Date
    Apr 2009
    Location
    Lincolnshire
    Posts
    3,014
    Thanks
    329
    Thanked 1,513 Times in 926
    Posts
    Blog Entries
    1

    Default Re: Do I need an uncoupling layer over new screed?

    Quote Originally Posted by Richard Edwards View Post
    Hi Ajax

    I'm always interested in your posts and read them front to back and again to digest them in detail

    Are you saying that if a standard screed was used in this case, say 75mm deep or deeper then as long as you left long enough time to fully dry out and commisioned the UFH properly prior to laying tiles, then a quality polymer modified ady - ie one part flex or standard high resin ady with polymer additive would be all that was needed and no need to use uncoupling mem. ?

    I like the advice about good practice - -sound !

    Essentially yes. I will qualify that though by saying a correctly used uncoupling membrane can add to the robustness of the system. they are also usefull where softer natural stone tiles are used as these are not capable of resisting som much expansion and contraction as say porcelaine or even ceramic.
    you must all buy this song from any good download site for just 79p. Proceeds to Blesma, RAFA and RAFBF charities



    Teresa Hind - The Fight Goes On

  20. #17
    giz
    Guest giz's Avatar

    Default Re: Do I need an uncoupling layer over new screed?

    Thanks for all the feedback, thoughts and detail - plenty to consider.
    On the plus side, none of this is in place yet so there is time to make adjustments - def worth signing in.
    Regarding the depth of screed - this started at 75mm but was adjusted by the architect to make the insulation numbers work with the rest of the build - more celotex less screed.
    I've read through all this and also had a conversation with my builder. Taking everything on board we will reduce the thickness of the insulation to 100mm (hidden from the inspectors!) and increase the screed depth to around 70-75mm.
    The final level will be driven by the track for the patio doors - build it up and stop at the right level
    Interesting comments about the expansion joints too. Is this a by product of the size of area? 9.4m x 3.3m = 31 sq-m (missed the typo in OP).
    Will a joint be necessary or just a precaution? I also presume you're talking about a joint in the screed not the tiling, wouldn't a gap be left between the tiles and the walls for this purpose?
    And if it makes a difference it's a north facing room.
    Given the use of a rapid set screed how long do you think I should leave it before comissioning the UFH and tiling - 28 days as reccomended by Ajax?
    I want it to last and work well but I'd also like to have a kitchen sometime in early November - screed can't go down before October 9th.
    However, if it needs to wait 4 weeks then so be it.

    Thanks
    Last edited by giz; 10-09-2010 at 11:07 AM.

  21. #18
    Established Tiler
    Richard Edwards's Avatar
    Join Date
    Mar 2009
    Location
    South Wales
    Posts
    375
    Thanks
    392
    Thanked 261 Times in 131
    Posts

    Smile Re: Do I need an uncoupling layer over new screed?

    Hi Giz

    Sounds like you heading down the right road now and as long at the screed quality is up to stratch and the tiling is to the correct standards you should be ok.

    Re - expansion joints, My thoughts are that as the area is only 3.3m wide but nearly 10m long then the issue is the length. It is on the cusp of a joint required. The very broad yardstick amongst the established tilers on here is a 50m2 limit - this assumes its roughly square. Your area is long and narrow and that increases the risk. If you decide to add an expansion joint - say half length, then this must be a full depth 'break' in the screed of approx 10-15mm wide. [Normally made by the screed layer with a piece of polystyrene foam / wood etc and extracted when fully cured.] An expansion joint in the tiled surface must be sited directly over the screed break. Use of a proper expansion joint - Shulter / Butec / Others with grout matching coloured silicone rubber insert 10mm will be the best - ribs in stainless steel / aluminium [Kitchen is better in SS if your pocket will allow].

    Ajax reading this post is the best guy to advise on time of curing / drying before commisioning although the longer the better. I advise my clients 8 weeks and bring the UFH up 5 deg / day and run it at normal op temp for 24 hours and then allow it to cool to room temp - Then we arrive and make a start on the tiling work.

    Hope this helps
    Richard Edwards - The Quality Tiling Co Ltd
    Where excellence comes as standard
    01443 206517 / 0778 626 7395
    www.thequalitytiling.co.uk -

Similar Threads

  1. how thick is the adhesive layer?
    By ChipRivers in forum Tile Adhesive, Grout and Substrate Preparation
    Replies: 4
    Last Post: 20-07-2009, 07:32 PM
  2. Advice sought on new screed, uncoupling membranes etc
    By mpphillips in forum Tanking & Wetrooms
    Replies: 6
    Last Post: 13-07-2009, 07:28 PM
  3. perma layer part2
    By div in forum Tiling Forum
    Replies: 0
    Last Post: 29-10-2008, 01:36 PM
  4. perma layer
    By div in forum Tiling Forum
    Replies: 6
    Last Post: 28-10-2008, 09:42 PM
  5. Foam layer under joists...
    By Rab78 in forum Tile Adhesive, Grout and Substrate Preparation
    Replies: 19
    Last Post: 16-08-2008, 09:07 PM

Visitors found this page by searching for:

uncoupling layer tiling

uncoupling layer

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Tilers Forums is the UK's largest wall and floor tiling forum. Advice is provided free of charge to all users. Tilers Forums does not take responsibility for any loss or damage caused due to following advice found on this forum. All wall and floor tiling should be carried out by a qualified wall and floor tiler. Views expressed on this forum are of the users and not Tilers Forums. Views expressed on this tiling forum are of the contributor only and not the forum as a whole. Not all views should be taken as fact but simply the opinion of the person posting. Readers are reminded to seek professional advice before undertaking any wall and floor tiling project.

Tilers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.
DMCA.com
[Output: 166.00 Kb. compressed to 149.72 Kb. by saving 16.27 Kb. (9.80%)]

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28