Discuss connect UFH to a socket? in the Electric Underfloor Heating at TilersForums; Hi there. I'm instaling a 3m UHF for a customer, and I've always powered all previous UFH from an RCD breaker (sparky doing the connection fom me). In this job ...
          
  1. #1
    New TilersForums Contributor masterbuilders's Avatar
    Join Date
    Dec 2009
    Location
    North London
    Posts
    17
    Thanks
    12
    Thanked 2 Times in 2
    Posts

    Question connect UFH to a socket?

    Hi there. I'm instaling a 3m UHF for a customer, and I've always powered all previous UFH from an RCD breaker (sparky doing the connection fom me). In this job the customer doesn't want the fuss of running a new wire from the consumer unit under the stairs to 1st floor bath, lifting floorboards etc.
    Is it possible, and above all is it legal, to power UHF from a socket using possibly a fuse box and fused thermostat? Any ideas welcome as my sparky is on holiday and cannot be contacted.

  2. #2
    Tilers Forums Arms Member
    Scott's Avatar
    Join Date
    Feb 2010
    Location
    Leighton Buzzard
    Posts
    4,170
    Thanks
    1,651
    Thanked 1,395 Times in 1,052
    Posts

    Default Re: connect UFH to a socket?

    It can be connected off the ring via an spur but not directly to a 13amp socket via a plug. How old is the consumer unit? Are the breakers up to date, RCD protected?
    aph257 likes this.

  3. The Following User Says Thank You to Scott For This Useful Post:

    masterbuilders (03-02-2011)

  4. #3
    New TilersForums Contributor masterbuilders's Avatar
    Join Date
    Dec 2009
    Location
    North London
    Posts
    17
    Thanks
    12
    Thanked 2 Times in 2
    Posts

    Default Re: connect UFH to a socket?

    thanks Scottley, thats good news then. Consumer unit is updated, less than 10 year old with full RCD protection

  5. #4
    Tilers Forums Arms Member
    Scott's Avatar
    Join Date
    Feb 2010
    Location
    Leighton Buzzard
    Posts
    4,170
    Thanks
    1,651
    Thanked 1,395 Times in 1,052
    Posts

    Default Re: connect UFH to a socket?

    If its RCD protected then it should be ok, but of course you will need to check that with your sparks, but is certainly deosnt have to go back to the board on its own circuit/radial.

  6. The Following User Says Thank You to Scott For This Useful Post:

    masterbuilders (04-02-2011)

  7. #5
    Tilers Forums Arms Member andy8758's Avatar
    Join Date
    Mar 2010
    Location
    Somerset
    Posts
    448
    Thanks
    36
    Thanked 128 Times in 96
    Posts

    Default Re: connect UFH to a socket?

    Depends on how big the installation is. Things to consider are:

    1. Total wattage of circuit - i.e. if wattage per sq m is 200 - you install 20 sq m in conservatory, thats a 4KW fixed load. What else is on that circuit? Will it overload it? Many ufh installations are in kitchen - you could end up with dishwasher and washing machine on same circuit - both have 3kw water heaters inside them. (yours is 3sq m not a problem on ring circuit).
    2. You must wire the installation through a fused spur, fuse appropriate to heating load. (Probably a 3A fuse in your case).
    3. Cables must be installed in a safe zone (directly vertical or horizontal to accessory) not within 50mm of gas or water pipe (although they can cross, just not run alongside).
    4. Only most recent electrical installations have a properly managed consumer unit with dual RCD breakers - system may require upgrading. You must be fully qualified to sort that out.
    5. Installation should include a plan of cable layout in floor (your responsibility) and a notice attached to consumer unit (this installation includes under floor heating....etc).

    In all honesty, the customer should be referred to an electrician, unless you got C & G 2381 qualification....
    aph257 likes this.

  8. The Following 2 Users Say Thank You to andy8758 For This Useful Post:

    Dan (08-02-2011), masterbuilders (08-02-2011)

  9. #6
    Tilers Forums Arms Member
    Scott's Avatar
    Join Date
    Feb 2010
    Location
    Leighton Buzzard
    Posts
    4,170
    Thanks
    1,651
    Thanked 1,395 Times in 1,052
    Posts

    Default Re: connect UFH to a socket?

    Or unless you get it signed off by building control.

  10. The Following User Says Thank You to Scott For This Useful Post:

    masterbuilders (08-02-2011)

  11. #7
    New TilersForums Contributor masterbuilders's Avatar
    Join Date
    Dec 2009
    Location
    North London
    Posts
    17
    Thanks
    12
    Thanked 2 Times in 2
    Posts

    Default Re: connect UFH to a socket?

    Thanks andy8758, I appreciate your reply, very informative.

Similar Threads

  1. socket extension screws
    By faithhealer in forum Tiling Forum
    Replies: 9
    Last Post: 26-08-2010, 04:59 PM
  2. Socket screws
    By klouan in forum Tiling Tools
    Replies: 40
    Last Post: 09-09-2008, 02:38 PM
  3. Splashback socket question
    By macten in forum Tiling Forum
    Replies: 11
    Last Post: 06-05-2008, 01:35 PM
  4. SOcket and see!
    By samwich in forum Tiling Forum
    Replies: 0
    Last Post: 04-03-2008, 08:30 PM

Visitors found this page by searching for:

underfloor heating c-130

ufh main fuse box

electric underfloor heating via plug socket

can you wire underfloor heating to a spur from a plug

ufh on kitchen circuit

can you power under floor heating off a mains socket spur

ufh socket

can floor heating be run from plug socket

wire underfloor heating to a plug

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Tilers Forums is the UK's largest wall and floor tiling forum. Advice is provided free of charge to all users. Tilers Forums does not take responsibility for any loss or damage caused due to following advice found on this forum. All wall and floor tiling should be carried out by a qualified wall and floor tiler. Views expressed on this forum are of the users and not Tilers Forums. Views expressed on this tiling forum are of the contributor only and not the forum as a whole. Not all views should be taken as fact but simply the opinion of the person posting. Readers are reminded to seek professional advice before undertaking any wall and floor tiling project.

Tilers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.
DMCA.com
[Output: 96.66 Kb. compressed to 88.09 Kb. by saving 8.57 Kb. (8.87%)]

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28