Help please, newly laid floor not getting very warm
Discuss Help please, newly laid floor not getting very warm in the Electric Underfloor Heating at Tilers Forum; Be gentle with me, this is my first post! Our newly installed ufh and cause of many many more grey hairs (long story involving having to completely remove the old ...- 23-12-2010 #1New Tiling Forum Contributor
- Join Date
- Nov 2010
- Posts
- 7
- Thanks
- 2
- Thanked 0 Times in 0
Posts
Help please, newly laid floor not getting very warm
Be gentle with me, this is my first post!
Our newly installed ufh and cause of many many more grey hairs (long story involving having to completely remove the old floor and replace)was finally installed and tiled over about a month ago. We used 10mm insulation boards under it and got an electrician to wire it in. All resistance values checked etc at every step of the way. Left it over 3 weeks to dry out etc and when we switched it on, it painfully slowly raised the temp to 7 deg C and no warmer. When I say painfully slowly I mean several hours, we then left it on overnight to see if it would improve but it still only got to a max of 7. Is this right? In which case it has been a complete waste of time and money and more, massive amounts of stress.
I really hope someone can advise? We have contacted the supplier who is being less than helpful.
Thanks for reading.
- 23-12-2010 #2Tool Hound



- Join Date
- Jan 2008
- Location
- Stourbridge, West Midlands
- Posts
- 21,159
- Thanks
- 1,696
- Thanked 5,986 Times in 3,909
Posts
Re: Help please, newly laid floor not getting very warm
Have you got more details, what make was it ? what wattage ?
Wall and floor tiler in the West Midlands, Dudley, Stourbridge. www.nptiling.co.uk
npitts@blueyonder.co.uk
- 23-12-2010 #3Tilers Forums Arms Member

- Join Date
- Aug 2010
- Location
- Dunfermline.
- Posts
- 4,746
- Thanks
- 437
- Thanked 1,204 Times in 965
Posts
What's the wattage if the mat.
Is that room temp or floor temp."The early bird catches the worm.... but it's the second mouse that gets the cheese"
- 23-12-2010 #4New Tiling Forum Contributor
- Join Date
- Nov 2010
- Posts
- 7
- Thanks
- 2
- Thanked 0 Times in 0
Posts
Re: Help please, newly laid floor not getting very warm
Hi, thanks for looking!
It is the floor temp, the room temp gets up to about 12 deg C. slightly higher if the radiator is on in the adjoining room.
It is a loose cable kit made by thermopads, TR3100 thermostat, ekoboard 10mm
- 23-12-2010 #5Tilers Forums Arms Member

- Join Date
- Apr 2009
- Location
- Tasmania
- Posts
- 8,022
- Thanks
- 3,965
- Thanked 1,990 Times in 1,587
Posts
Re: Help please, newly laid floor not getting very warm
how was the probe fitted and welcome to the forum
- 23-12-2010 #6New Tiling Forum Contributor
- Join Date
- Nov 2010
- Posts
- 7
- Thanks
- 2
- Thanked 0 Times in 0
Posts
Re: Help please, newly laid floor not getting very warm
Thank you :-)
Ummm, probe fitted into floor, I remember hubby dug out a groove for it?
Forgot to say cables were 65mm apart so wattage 150 I think...am I right in thinking the wattage varies according to how close together the cables are?
- 23-12-2010 #7Tilers Forums Arms Member

- Join Date
- Aug 2010
- Location
- Dunfermline.
- Posts
- 4,746
- Thanks
- 437
- Thanked 1,204 Times in 965
Posts
How far apart were the cables installed.
Did you put self levelling compound over cable."The early bird catches the worm.... but it's the second mouse that gets the cheese"
- 23-12-2010 #8New Tiling Forum Contributor
- Join Date
- Nov 2010
- Posts
- 7
- Thanks
- 2
- Thanked 0 Times in 0
Posts
Re: Help please, newly laid floor not getting very warm
hiya, 65mm and yes we did.
- 23-12-2010 #9Tilers Forum Trusted Member


- Join Date
- May 2007
- Location
- Stockton-on-Tees
- Posts
- 3,506
- Thanks
- 520
- Thanked 967 Times in 803
Posts
Re: Help please, newly laid floor not getting very warm
How big is the floor area, what size kit was installed and have you checked the thermostat settings ?
- 23-12-2010 #10Tilers Forums Arms Member

- Join Date
- Apr 2009
- Location
- Tasmania
- Posts
- 8,022
- Thanks
- 3,965
- Thanked 1,990 Times in 1,587
Posts
Re: Help please, newly laid floor not getting very warm
is the probe under insulatiom board and do any wires cross over or run near the probe
- 23-12-2010 #11Tilers Forums Arms Member

- Join Date
- Aug 2010
- Location
- Dunfermline.
- Posts
- 4,746
- Thanks
- 437
- Thanked 1,204 Times in 965
Posts
That's works out at a 150 watt, and should be suitable to heat the floor to 25+ degrees easily. Is the thermostat in the room that's tiled or outside in adjoining room.
"The early bird catches the worm.... but it's the second mouse that gets the cheese"
-
The Following User Says Thank You to Stewart For This Useful Post:
JaneJ (23-12-2010)
- 23-12-2010 #12Tool Hound



- Join Date
- Jan 2008
- Location
- Stourbridge, West Midlands
- Posts
- 21,159
- Thanks
- 1,696
- Thanked 5,986 Times in 3,909
Posts
Re: Help please, newly laid floor not getting very warm
Not really the done thing but I would be inclined to rule out the 3 items that can go wrong, the thermostat probe, the controller and the heating element itself. You can do thisby bypassing the controller and probe. this is done by connecting a plug to the power cable and feeding power direct to cable.
Please note that this should be done by a qualified electrician.Wall and floor tiler in the West Midlands, Dudley, Stourbridge. www.nptiling.co.uk
npitts@blueyonder.co.uk
- 23-12-2010 #13Tilers Forums Arms Member

- Join Date
- Aug 2010
- Location
- Dunfermline.
- Posts
- 4,746
- Thanks
- 437
- Thanked 1,204 Times in 965
Posts
Also.... Are there any heating pipes running near the probe under the floor.
"The early bird catches the worm.... but it's the second mouse that gets the cheese"
-
The Following User Says Thank You to Stewart For This Useful Post:
Scott (23-12-2010)
- 23-12-2010 #14Tool Hound



- Join Date
- Jan 2008
- Location
- Stourbridge, West Midlands
- Posts
- 21,159
- Thanks
- 1,696
- Thanked 5,986 Times in 3,909
Posts
Wall and floor tiler in the West Midlands, Dudley, Stourbridge. www.nptiling.co.uk
npitts@blueyonder.co.uk
- 23-12-2010 #15New Tiling Forum Contributor
- Join Date
- Nov 2010
- Posts
- 7
- Thanks
- 2
- Thanked 0 Times in 0
Posts
Re: Help please, newly laid floor not getting very warm
OK...
floor area approx 7.5m2, cable was from memory 115m, kit was for 6.9-8.8m2
How do you check the thermostat settings? I haven't programmed it, only used it on manual. If I set the room temp to 18-20 deg C the floor comes on and runs constantly but floor temp never gets above 7 deg 9well it did make 8 once briefly!)
I think the probe was grooved into the insulation boards, no wires crossing anywhere and I'm not sure how near to the probe, will have to ask hubby that one.
Thermostat is in the room that the UFH is in
Pretty sure no heating pipes as we took the floor out to bare earth and beyond so pipes would have been fairly obvious even to me!
Hubby did suggest by passing the thermostat, will get the electrician back in.
If the probe was faulty, ie reading a faulty temp surely the floor would get much warmer than it does as it continues to feed power to the cables? I know it is putting power in as my electric watch thingy goes up when it is on and down when it isn't. How would I know if the thermostat was faulty? It doesn't make any sense to me that power is going in but it isn't getting any warmer??
- 23-12-2010 #16Tool Hound



- Join Date
- Jan 2008
- Location
- Stourbridge, West Midlands
- Posts
- 21,159
- Thanks
- 1,696
- Thanked 5,986 Times in 3,909
Posts
Re: Help please, newly laid floor not getting very warm
I really would try adding a plug to the cable and powering direct 1st. This will isolate or highlight the problem area.
As for the probe, was it inserted into a tube or direct int the insulation. Its always better to use the tube as its simply a matter of pulling one probe out and then re inserting the new one should problems arise.
What has the heating company actually said ?Wall and floor tiler in the West Midlands, Dudley, Stourbridge. www.nptiling.co.uk
npitts@blueyonder.co.uk
-
The Following User Says Thank You to Sir Ramic For This Useful Post:
JaneJ (23-12-2010)
- 23-12-2010 #17Tilers Forum Trusted Member


- Join Date
- May 2007
- Location
- Stockton-on-Tees
- Posts
- 3,506
- Thanks
- 520
- Thanked 967 Times in 803
Posts
Re: Help please, newly laid floor not getting very warm
If you could watch the electric watchdog thing and operate the stat up and down you should see a rise and fall in demand as the stat kicks in and out.
- 23-12-2010 #18doug boardleyGuest
- 23-12-2010 #19New Tiling Forum Contributor
- Join Date
- Nov 2010
- Posts
- 7
- Thanks
- 2
- Thanked 0 Times in 0
Posts
Re: Help please, newly laid floor not getting very warm
Ok, it has been wired up for over an hour and a half and it is not getting any warmer than it did with the thermostat and probe in the circuit.
HELP! Does this mean the cable is dodgy? It is getting warm but hardly and slowly.
In answer to the watchdog thing, it doesn't kick in and out cos it never gets anywhere near the set temp.
- 23-12-2010 #20Tilers Forums Arms Member

- Join Date
- Aug 2010
- Location
- Dunfermline.
- Posts
- 4,746
- Thanks
- 437
- Thanked 1,204 Times in 965
Posts
Does that particular thermostat have a separate setting for maximum temp as with some of heat-com ones, also have you tried changing the thermostat to room temp?
"The early bird catches the worm.... but it's the second mouse that gets the cheese"
- 23-12-2010 #21Tilers Forums Arms Member

- Join Date
- Aug 2010
- Location
- Dunfermline.
- Posts
- 4,746
- Thanks
- 437
- Thanked 1,204 Times in 965
Posts
Sorry just re- read previous post so please ignore
"The early bird catches the worm.... but it's the second mouse that gets the cheese"
- 24-12-2010 #22Tiling Forum Contributor
- Join Date
- Dec 2008
- Location
- Wolverhampton
- Posts
- 85
- Thanks
- 12
- Thanked 10 Times in 10
Posts
Re: Help please, newly laid floor not getting very warm
Hi,
I would find out from the manufacturer what the resistance value is for your specific kit and get it re checked by your electrician or yourself. If you have the floor directly wired to a plug and the floor is not getting up to temperature. It’s pointing towards a fault with the under floor wiring . sorry
- 24-12-2010 #23Tilers Forums Arms Member

- Join Date
- Apr 2007
- Location
- Sedgefield
- Posts
- 8,280
- Thanks
- 2,527
- Thanked 2,472 Times in 2,006
Posts
Re: Help please, newly laid floor not getting very warm
only thing I can think of now is if the tiles were dot and dabbed so there is poor heat transferance.
- 24-12-2010 #24New Tiling Forum Contributor
- Join Date
- Nov 2010
- Posts
- 7
- Thanks
- 2
- Thanked 0 Times in 0
Posts
Re: Help please, newly laid floor not getting very warm
Arrgghhh! does that mean we can't do anything about it? What is dot and dab?
- 24-12-2010 #25Tilers Forums Arms Member

- Join Date
- Apr 2007
- Location
- Sedgefield
- Posts
- 8,280
- Thanks
- 2,527
- Thanked 2,472 Times in 2,006
Posts
Re: Help please, newly laid floor not getting very warm
Hi jane, dot and dab is where the adhesive is put on the tile in 'dollops' (usually one in each corner and maybe one in the middle) instead of full coverage using a trowel. The heat can only pass where the adhesive is, hope you follow. Checked out the manufacturer, seem a big outfit. Would check resistance etc out and get back
Similar Threads
-
Tiling on to newly laid concrete.
By Perfectly Tiled in forum Tile Adhesive and GroutReplies: 1Last Post: 19-11-2009, 03:43 PM -
Newly laid ceramic tile floor
By mairihutton in forum New Members Say Hi HereReplies: 30Last Post: 24-09-2009, 09:27 AM -
Newly laid porcelain tiles too easy to remove
By Audrey Campbell in forum Guest AreaReplies: 8Last Post: 06-12-2008, 12:09 AM -
Newly laid floor tiles lifting
By Aneles in forum Tiling ForumReplies: 7Last Post: 13-06-2007, 07:54 PM


LinkBack URL
About LinkBacks

Reply With Quote















do tiles have a use by date?
19 Minutes Ago in Tiling Forum