Discuss Under Floor Heating on Marley tiles - That's a Hot One! in the Electric Underfloor Heating at TilersForums; I need suggestions on your approach in tiling over Marley tiles (80s). The customer wants U.F.H. Here is the situation: There was no mentioning of UFH until I nearly finished ...
          
  1. #1
    Tilers Forums Arms Member SnipSnap's Avatar
    Join Date
    Mar 2008
    Location
    Oxford
    Posts
    141
    Thanks
    7
    Thanked 9 Times in 9
    Posts

    Default Under Floor Heating on Marley tiles - That's a Hot One!

    I need suggestions on your approach in tiling over Marley tiles (80s). The customer wants U.F.H.

    Here is the situation:
    There was no mentioning of UFH until I nearly finished prepping the floor with Multibase (main substrate is screed). The floor was nasty, and managed to smooth it out (mostly) with two application of the SLC.

    50% of the floor has a SLC thickness varying between 6 - 12mm, with the thinnest section to another 30% of the floor going to a couple of millimetres.
    The rest is feathered to nothing, you can see the old Marley tiles.

    If I knew in advance, I would have stripped the tiles off, hired a scrabbler and mechanically removed the black glue, then applied the SLC and tiled.

    Now, what would you do in my situation?

    1) Apply yet another 6mm of SLC?
    2) Board off the floor with ..................?
    3) Overlay with Ditra matting?

    Consider that I usually apply 2 coats of SLC after the cable has been installed.

    Over to you people.

  2. #2
    Tool Hound


    Sir Ramic's Avatar
    Join Date
    Jan 2008
    Location
    Stourbridge, West Midlands
    Posts
    16,496
    Thanks
    1,471
    Thanked 5,598 Times in 3,560
    Posts
    Blog Entries
    2

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    I would remove the Marley tiles and then SLC again all over.
    Wall and floor tiler in the West Midlands, Dudley, Stourbridge. www.nptiling.co.uk

  3. The Following 2 Users Say Thank You to Sir Ramic For This Useful Post:

    jay (27-11-2010), SandyFloor (27-11-2010)

  4. #3
    Tilers Forums Arms Member SnipSnap's Avatar
    Join Date
    Mar 2008
    Location
    Oxford
    Posts
    141
    Thanks
    7
    Thanked 9 Times in 9
    Posts

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    Quote Originally Posted by Sir Ramic View Post
    I would remove the Marley tiles and then SLC again all over.
    Thanks Sir!
    Are you suggesting the above on the section where the marley tiles are visible or do you mean ALL of the floor. Kitchen units have now been installed so complete removal is not viable.

  5. #4
    Tilers Forums Arms Member SandyFloor's Avatar
    Join Date
    Sep 2009
    Location
    Ayrshire
    Posts
    2,380
    Thanks
    453
    Thanked 1,002 Times in 677
    Posts

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    The first thing that jumped into my head is I often remove marley tiles with a heat gun and you're talking about putting a heating mat on top of them. I don't know what would happen there.

  6. #5
    Tilers Forums Arms Member
    diamondtiling's Avatar
    Join Date
    Jun 2009
    Location
    cheshire
    Posts
    6,859
    Thanks
    4,735
    Thanked 3,022 Times in 1,991
    Posts

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    You should have removed the marleys first mate.

  7. The Following User Says Thank You to diamondtiling For This Useful Post:

    SandyFloor (27-11-2010)

  8. #6
    Administrator


    Dave's Avatar
    Join Date
    May 2007
    Location
    County Durham
    Posts
    54,385
    Thanks
    9,717
    Thanked 14,137 Times in 9,985
    Posts
    Blog Entries
    1

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    I would install insulation boards.. best to heat just the tiles and not the slab as well..

  9. #7
    Tilers Forums Arms Member
    faithhealer's Avatar
    Join Date
    Apr 2007
    Location
    Sedgefield
    Posts
    8,280
    Thanks
    2,527
    Thanked 2,472 Times in 2,006
    Posts

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    Quote Originally Posted by SandyFloor View Post
    The first thing that jumped into my head is I often remove marley tiles with a heat gun and you're talking about putting a heating mat on top of them. I don't know what would happen there.
    my first thought too

  10. #8
    Tilers Forums Arms Member SnipSnap's Avatar
    Join Date
    Mar 2008
    Location
    Oxford
    Posts
    141
    Thanks
    7
    Thanked 9 Times in 9
    Posts

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    Quote Originally Posted by diamondtiling View Post
    You should have removed the marleys first mate.
    I was not told of any UFH prior to it hence the reason for not removing them.

  11. #9
    Tilers Forums Arms Member SnipSnap's Avatar
    Join Date
    Mar 2008
    Location
    Oxford
    Posts
    141
    Thanks
    7
    Thanked 9 Times in 9
    Posts

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    Quote Originally Posted by Dave View Post
    I would install insulation boards.. best to heat just the tiles and not the slab as well..
    That's my feeling too mate.

    I was told by a local tile shop that I could use Ditra matting but I do not like that idea.

    Which type of insulation board would you suggest Dave? It needs the thinnest possible though!

    Another thing... I am not sure of what wattage the element it's gona be... I assume that it is for warming the floor only and not as a main source of heating.

  12. #10
    Administrator


    Dave's Avatar
    Join Date
    May 2007
    Location
    County Durham
    Posts
    54,385
    Thanks
    9,717
    Thanked 14,137 Times in 9,985
    Posts
    Blog Entries
    1

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    IMO 10mm min.. but you can get 6mm if height is an issue.. You have loads of choice really to buy from... Uheat do their's and wedi or warmup etc etc..

    Ditra will not insulate a floor..

  13. The Following User Says Thank You to Dave For This Useful Post:

    SnipSnap (27-11-2010)

  14. #11
    Tilers Forums Arms Member SnipSnap's Avatar
    Join Date
    Mar 2008
    Location
    Oxford
    Posts
    141
    Thanks
    7
    Thanked 9 Times in 9
    Posts

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    Quote Originally Posted by Dave View Post
    ...Ditra will not insulate a floor..
    I knew that, that's why I was not convinced on using it.

    If the UFH is low wattage I should be fine with the 6 mm, the heat transfer should be minimum. I will be removing a section of Marley tiles up to where the existing levelling compound is to a depth of 6.

  15. #12
    Administrator


    Dave's Avatar
    Join Date
    May 2007
    Location
    County Durham
    Posts
    54,385
    Thanks
    9,717
    Thanked 14,137 Times in 9,985
    Posts
    Blog Entries
    1

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    would the extra 4mm make any difference franco.. 10mm will help with heat loss that's all mate..

  16. #13
    Tilers Forums Arms Member SnipSnap's Avatar
    Join Date
    Mar 2008
    Location
    Oxford
    Posts
    141
    Thanks
    7
    Thanked 9 Times in 9
    Posts

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    Quote Originally Posted by Dave View Post
    would the extra 4mm make any difference franco.. 10mm will help with heat loss that's all mate..
    Assuming that the board is 6 mm, the cable is 4 mm thick, the SLC 5 mm (over the cable), the adhesive 6mm, then the thickness of the tile 8 - 10mm.

    We are looking at a minimum 29-31 mm, so looking at that, another extra 4 mm can take it to 35 mm visible at the door.

    Before anyone comments on the 5mm top levelling... I always do this for cable protection as once had to replace a tile that had a small glaze blemish on it... that made me swet a bit... when I had to Multimaster the old ahesive off and got to see the red cable coming through. So, the 5 mm extra self levelling will be applied. LOL

    I will have to discuss it with my contractor first.

  17. The Following User Says Thank You to SnipSnap For This Useful Post:

    Dave (27-11-2010)

  18. #14
    Administrator


    Dave's Avatar
    Join Date
    May 2007
    Location
    County Durham
    Posts
    54,385
    Thanks
    9,717
    Thanked 14,137 Times in 9,985
    Posts
    Blog Entries
    1

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    I think you will get the adhesive to compress to 3mm..lol

  19. #15
    Tilers Forums Arms Member SnipSnap's Avatar
    Join Date
    Mar 2008
    Location
    Oxford
    Posts
    141
    Thanks
    7
    Thanked 9 Times in 9
    Posts

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    Yeah, sure but you know how it is... always allow for a little more... than less.

  20. #16
    Administrator


    Dave's Avatar
    Join Date
    May 2007
    Location
    County Durham
    Posts
    54,385
    Thanks
    9,717
    Thanked 14,137 Times in 9,985
    Posts
    Blog Entries
    1

    Default Re: Under Floor Heating on Marley tiles - That's a Hot One!

    Let us know which way you go, perhaps with a few pics hey!!

Similar Threads

  1. Marley Floor Tiles
    By curlycan in forum Tiling Forum
    Replies: 2
    Last Post: 12-10-2009, 07:57 PM
  2. marley tiles on floor help?
    By mps in forum Tile Adhesive, Grout and Substrate Preparation
    Replies: 5
    Last Post: 23-09-2009, 10:09 AM
  3. New Marley Floor Tiles
    By Amtiler in forum Tile Adhesive, Grout and Substrate Preparation
    Replies: 11
    Last Post: 24-11-2008, 01:42 PM
  4. Replies: 3
    Last Post: 16-11-2007, 09:33 PM

Visitors found this page by searching for:

can you tile over marley tiles and put under tile heating

old marley floor tiles sweat

electric underfloor heating low wattage

marley floor tiles

underfloor heating marley tiles

do you put underfloor heating under kitchen units

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Tilers Forums is the UK's largest wall and floor tiling forum. Advice is provided free of charge to all users. Tilers Forums does not take responsibility for any loss or damage caused due to following advice found on this forum. All wall and floor tiling should be carried out by a qualified wall and floor tiler. Views expressed on this forum are of the users and not Tilers Forums. Views expressed on this tiling forum are of the contributor only and not the forum as a whole. Not all views should be taken as fact but simply the opinion of the person posting. Readers are reminded to seek professional advice before undertaking any wall and floor tiling project.

Tilers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.
DMCA.com
[Output: 164.89 Kb. compressed to 149.19 Kb. by saving 15.70 Kb. (9.52%)]

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28