Discuss UFH Height, Transition to Adjacent Flooring in the Electric Underfloor Heating at TilersForums; Hi all I have been working out my new floor height when I have installed my UFH in the bathroom. 3mm Adhesive 10mm Thermopanel 6mm Self levelling compound (containing the ...
          
  1. #1
    TilersForums Contributor mmmadman's Avatar
    Join Date
    Jun 2010
    Location
    York
    Posts
    73
    Thanks
    66
    Thanked 10 Times in 4
    Posts

    Default UFH Height, Transition to Adjacent Flooring

    Hi all

    I have been working out my new floor height when I have installed my UFH in the bathroom.

    3mm Adhesive
    10mm Thermopanel
    6mm Self levelling compound (containing the UFH wire)
    4mm Adhesive
    6mm Tile

    That adds up to 29mm, I will need a chuffing lift to get into the bathroom from the hallway.................!!!!

    There used to be carpet in the bathroom @ around a thickness of 10mm so its a big differance.

    What do you guys & gals do to overcome this or do you just fit a ramp or somthing.......?????!!!!!!!????

    Many thanks

    Cheers.............

  2. #2
    Dan
    Dan is offline
    Tilers Forums Admin Dan's Avatar
    Join Date
    Apr 2006
    Location
    Staffordshire, UK
    Posts
    19,228
    Thanks
    7,721
    Thanked 5,034 Times in 2,883
    Posts
    Blog Entries
    6

    Default Re: UFH Height, Transition to Adjacent Flooring

    It's always difficult to ensure you're getting the most equal level possible in situations like this, but it isn't always possible to get them exact, without lifting the other floor, obviously.

    I'd consider going to Underfloor Heating | Electric | Floor Insulation | Uheat and getting 6mm insulation, and using their 3mm cable you'll only need 4mm or so levelling compound.

    Then with what height difference you have left you may be able to use a standard screwed door trim which would leave a small ramp. Or I've made wooden versions before that look smart varnished or whatever, and screw that to the floor.

    To be honest it's a common problem and there's never an easy solution.
    Dan
    TilersForums.co.uk Owner
    The UK's biggest Tiling Forum

    Like TF? Try our other forums: The UK's biggest Electrical Forum, The UK's biggest Plumbing Forum, The UK's biggest Flooring Forum. Some newer trade-related forums; Plastering Forum, Building Forum, Decorating Forum.
    Follow TilersForums on Twitter.


  3. #3
    Tilers Forums Arms Member
    diamondtiling's Avatar
    Join Date
    Jun 2009
    Location
    cheshire
    Posts
    6,859
    Thanks
    4,735
    Thanked 3,022 Times in 1,991
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    Take up the chipboard/floorboards, relay with 18mm ply, fit insulation, heating and tiles.

    Bobs your uncle.
























    (unless you don't have an uncle bob, in that case Fanny's your Aunt unless you don't have an Aunt Fanny either)


  4. #4
    Dan
    Dan is offline
    Tilers Forums Admin Dan's Avatar
    Join Date
    Apr 2006
    Location
    Staffordshire, UK
    Posts
    19,228
    Thanks
    7,721
    Thanked 5,034 Times in 2,883
    Posts
    Blog Entries
    6

    Default Re: UFH Height, Transition to Adjacent Flooring

    What thickness are the floorboards? Good point that Dom!
    Dan
    TilersForums.co.uk Owner
    The UK's biggest Tiling Forum

    Like TF? Try our other forums: The UK's biggest Electrical Forum, The UK's biggest Plumbing Forum, The UK's biggest Flooring Forum. Some newer trade-related forums; Plastering Forum, Building Forum, Decorating Forum.
    Follow TilersForums on Twitter.


  5. The Following User Says Thank You to Dan For This Useful Post:

    diamondtiling (25-08-2010)

  6. #5
    TilersForums Contributor mmmadman's Avatar
    Join Date
    Jun 2010
    Location
    York
    Posts
    73
    Thanks
    66
    Thanked 10 Times in 4
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    Quote Originally Posted by Dan View Post
    I'd consider going to Underfloor Heating | Electric | Floor Insulation | Uheat and getting 6mm insulation, and using their 3mm cable you'll only need 4mm or so levelling compound.
    I got a very good quote from U Heat and have exchanged a few emails with them, very helpfull by the way and they recommended the 10mm board & loose wire installation which is 4.3mm thick, I would then pore self levelling compound over this to seal it.
    The room is only 3m sq but the toilet is set at an angle in a corner so I guess the wire system was better suited to my install.

    The existing floor is approx 18mm tongue & groove boards. If I relayed the floor in 18mm ply could I then use a 6mm insulation board, mind you only saving 4mm for the price of a couple of sheets of ply......!!!

    I thought about laying the wire then spreading the adhesive and laying the tiles but would not be able to gaurantee an equal coating of adhesive, plus the issue of the wire getting damaged.......!!!!

    Why did I suggest to the wife it would be nice to have UFH.....

    Thanks gents....................

  7. #6
    Tilers Forums Arms Member
    diamondtiling's Avatar
    Join Date
    Jun 2009
    Location
    cheshire
    Posts
    6,859
    Thanks
    4,735
    Thanked 3,022 Times in 1,991
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    T&G boards is not suitable to tile onto at all, fixing 10mm insulation boards wont add any strength either. The correct prep now will save you money in the long term.
    As for the height difference I spray glue extra thick underlay right outside the door, refit the existing underlay and carpet and use a doorway trim that allows for two different heights.


  8. #7
    TilersForums Contributor mmmadman's Avatar
    Join Date
    Jun 2010
    Location
    York
    Posts
    73
    Thanks
    66
    Thanked 10 Times in 4
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    Quote Originally Posted by diamondtiling View Post
    Take up the chipboard/floorboards, relay with 18mm ply, fit insulation, heating and tiles.
    So is this order correct, from the tile down this time:

    6mm Tile
    4mm Flexible Addy
    6mm SLC (including UFH wire)
    6mm Ekoboard insulating board
    3mm Flexible Addy
    18mm Ply floor

    That's down to 25mm total thickness which is getting better I guess.

    Ive heard of many people tiling over tongue and grooved floor boards after covering with a cement based board, is this bad practice.../

    Cheers.......

  9. #8
    Tilers Forums Arms Member
    diamondtiling's Avatar
    Join Date
    Jun 2009
    Location
    cheshire
    Posts
    6,859
    Thanks
    4,735
    Thanked 3,022 Times in 1,991
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    What size trowel are you using for your tiles? 10mm at least.

  10. #9
    TilersForums Contributor mmmadman's Avatar
    Join Date
    Jun 2010
    Location
    York
    Posts
    73
    Thanks
    66
    Thanked 10 Times in 4
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    Not sure what trowel to use as I have never done a tiled floor before, well except my natural slate patio I have just finished.

    Is 10mm the norm for floor tiles then?


    Cheers..............

  11. #10
    Tilers Forums Arms Member
    diamondtiling's Avatar
    Join Date
    Jun 2009
    Location
    cheshire
    Posts
    6,859
    Thanks
    4,735
    Thanked 3,022 Times in 1,991
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    10mm will give you the coverage you need on the tiles, depending on what size they are they may need to be back skimmed as well.

  12. #11
    Houston
    Guest Houston's Avatar

    Default Re: UFH Height, Transition to Adjacent Flooring

    u can tile onto 18mm t/g boards just make sure thier screwed down

  13. #12
    pjc
    pjc is offline
    TilersForums Trusted Member

    pjc's Avatar
    Join Date
    Oct 2007
    Location
    high wycombe
    Posts
    4,179
    Thanks
    244
    Thanked 688 Times in 537
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    as Dave had said but i use grpfill to fix them

  14. #13
    TilersForums Trusted Member


    Phil Hobson's Avatar
    Join Date
    Aug 2009
    Location
    oldham
    Posts
    7,212
    Thanks
    5,124
    Thanked 3,112 Times in 1,922
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    Quote Originally Posted by Houston View Post
    u can tile onto 18mm t/g boards just make sure thier screwed down

    ??????? I would beg to differ

  15. The Following User Says Thank You to Phil Hobson For This Useful Post:


  16. #14
    doug boardley
    Guest doug boardley's Avatar

    Default Re: UFH Height, Transition to Adjacent Flooring

    Quote Originally Posted by Phil Hobson View Post
    ??????? I would beg to differ
    me too Phil

  17. The Following User Says Thank You to doug boardley For This Useful Post:

    Phil Hobson (29-08-2010)

  18. #15
    Houston
    Guest Houston's Avatar

    Default Re: UFH Height, Transition to Adjacent Flooring

    y Phill & Doug

  19. #16
    Houston
    Guest Houston's Avatar

    Default Re: UFH Height, Transition to Adjacent Flooring

    sorry and diamond tiling

  20. #17
    TilersForums Trusted Member


    Phil Hobson's Avatar
    Join Date
    Aug 2009
    Location
    oldham
    Posts
    7,212
    Thanks
    5,124
    Thanked 3,112 Times in 1,922
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    T&G is not a suitable substate for tiles, never was never will be!, overboard with min 15mm ply and to be sure, glue and screw backerboard. That way no probs, providing there is no deflection in the floor

  21. The Following User Says Thank You to Phil Hobson For This Useful Post:

    mmmadman (31-08-2010)

  22. #18
    Houston
    Guest Houston's Avatar

    Default Re: UFH Height, Transition to Adjacent Flooring

    Phil, i think you are wrong. If T&G boards are rigid screwed to joists and sometimes you might need some extra noggins its not a problem. Bal & Granfix do adhesives for T&G that i have used over the years and no probs

  23. #19
    TilersForums Trusted Member


    Phil Hobson's Avatar
    Join Date
    Aug 2009
    Location
    oldham
    Posts
    7,212
    Thanks
    5,124
    Thanked 3,112 Times in 1,922
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    We all have the right to our own opinions mate, but we are not doing this forum any good by giving bad advice. I stand by what I said re: T&G. I am well aware of the products you mention. I would never tile directly onto T&G

  24. #20
    Houston
    Guest Houston's Avatar

    Default Re: UFH Height, Transition to Adjacent Flooring

    phill its not bad advice its fact, u can tile on T&G boards.

  25. #21
    pjc
    pjc is offline
    TilersForums Trusted Member

    pjc's Avatar
    Join Date
    Oct 2007
    Location
    high wycombe
    Posts
    4,179
    Thanks
    244
    Thanked 688 Times in 537
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    Quote Originally Posted by Houston View Post
    Phil, i think you are wrong. If T&G boards are rigid screwed to joists and sometimes you might need some extra noggins its not a problem. Bal & Granfix do adhesives for T&G that i have used over the years and no probs
    one of these company's used to have lots of probs and changed the goalposts overnight to having 30 cmts centers on joists i only ever have that in the commercial market with 40mm thick chipboard or tg ply i have seen lots of problems over the years direct on floorboards with the said adhesive some of the smaller floors i have seen had survived but i wouldn't take the risk after 28 years of tiling and the adhesive named will blame you without a doubt if there is any probs they will run a mile believe me they will not take any blame

  26. The Following User Says Thank You to pjc For This Useful Post:

    Phil Hobson (29-08-2010)

  27. #22
    TilersForums Trusted Member


    Phil Hobson's Avatar
    Join Date
    Aug 2009
    Location
    oldham
    Posts
    7,212
    Thanks
    5,124
    Thanked 3,112 Times in 1,922
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    Quote Originally Posted by Houston View Post
    phill its not bad advice its fact, u can tile on T&G boards.

    I wasn't having a pop at you Houston, It's just something I would never do. As above adhesive manufacturers bring out these easy fix, no prep all singing, all dancing adhesives. Then when the proverbial hits the fan they don't want to know. In my 43yrs experience in tiling in the UK and abroad, I have never/will never tile directly to T&G. Just my opinion
    Last edited by Phil Hobson; 29-08-2010 at 07:34 PM.

  28. The Following User Says Thank You to Phil Hobson For This Useful Post:

    Rob Z (29-08-2010)

  29. #23
    Tilers Forums Arms Member
    Rob Z's Avatar
    Join Date
    Oct 2007
    Location
    Virginia USA
    Posts
    3,729
    Thanks
    1,524
    Thanked 1,971 Times in 1,195
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    With wood's tendency to expand so much across its width, I can't imagine getting a stable floor built of T&G strip flooring. Something needs to go over it to isolate the tile from the movement of the wood flooring.

    We're on a job now which had tile set straight over T&G flooring. All three bathrooms had problems, the kitchen was so-so. Not a good track record for tile on T&G in that house.

  30. The Following User Says Thank You to Rob Z For This Useful Post:

    Phil Hobson (29-08-2010)

  31. #24
    New TilersForums Contributor leenco12's Avatar
    Join Date
    Sep 2010
    Posts
    1
    Thanks
    0
    Thanked 0 Times in 0
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    Quote Originally Posted by mmmadman View Post
    I got a very good quote from U Heat and have exchanged a few emails with them, very helpfull by the way and they recommended the 10mm board & loose wire installation which is 4.3mm thick, I would then pore self levelling compound over this to seal it.
    The room is only 3m sq but the toilet is set at an angle in a corner so I guess the wire system was better suited to my install.

    The existing floor is approx 18mm tongue & groove boards. If I relayed the floor in 18mm ply could I then use a 6mm insulation board, mind you only saving 4mm for the price of a couple of sheets of ply......!!!

    I thought about laying the wire then spreading the adhesive and laying the tiles but would not be able to gaurantee an equal coating of adhesive, plus the issue of the wire getting damaged.......!!!!

    Why did I suggest to the wife it would be nice to have UFH.....

    Thanks gents....................
    T&G boards is not suitable to tile onto at all, fixing 10mm insulation boards wont add any strength either. The correct prep now will save you money in the long term.
    As for the height difference I spray glue extra thick underlay right outside the door, refit the existing underlay and carpet and use a doorway trim that allows for two different heights.

    __________________
    watch movies online
    Last edited by leenco12; 14-09-2010 at 04:26 AM.

  32. #25
    Houston
    Guest Houston's Avatar

    Default Re: UFH Height, Transition to Adjacent Flooring

    its all in the prep

  33. #26
    Established Tiler
    Ken Bruty's Avatar
    Join Date
    Sep 2009
    Location
    Wellingborough, Northants
    Posts
    1,632
    Thanks
    976
    Thanked 500 Times in 393
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    Houston, I have to agree with the others re: the t&g from a bad personal experience, where I was asked by my customer to tile onto t&g which I screwed really tight. The issue was height, because the front door was a pvc one and couldn't be trimmed at the bottom to accomodate any extra height that overboarding would cause, so I advised it best not to tile at all, but they were insistent, and, instead of walking away I gave in. Having done the job, I was waiting for the phone call, and sure enough in 3 months time - "can you replace 6 tiles that have cracked please" I got paid for it, but I was really uncomfortable doing this knowing that it would probably go again, which it did, but on the upside I could have been employed there full time replacing them when they went, but you just can't say told you so. The moral of the story is that I would NEVER do this again for anyone, I'd rather walk away from it in future. I have to say I think you have been lucky so far, I only did it the once. But we will all do things differently, that's what makes us human.
    Tilers in Bedfordshire, Tilers in Northamptonshire, Tilers in Buckinghamshire
    www.kdbceramicsandstone.com

  34. #27
    Houston
    Guest Houston's Avatar

    Default Re: UFH Height, Transition to Adjacent Flooring

    Mr Bruty, its got nothing to do with luck, its all in the prep!

  35. #28
    doug boardley
    Guest doug boardley's Avatar

    Default Re: UFH Height, Transition to Adjacent Flooring

    Quote Originally Posted by Houston View Post
    Phil, i think you are wrong. If T&G boards are rigid screwed to joists and sometimes you might need some extra noggins its not a problem. Bal & Granfix do adhesives for T&G that i have used over the years and no probs
    hve you seen what happens to T&G flooring after plasterers have been in???? the edges curl up! just imagine those edges
    curling up under your tiles!!

  36. The Following User Says Thank You to doug boardley For This Useful Post:

    Phil Hobson (17-09-2010)

  37. #29
    TilersForums Trusted Member


    Phil Hobson's Avatar
    Join Date
    Aug 2009
    Location
    oldham
    Posts
    7,212
    Thanks
    5,124
    Thanked 3,112 Times in 1,922
    Posts

    Default Re: UFH Height, Transition to Adjacent Flooring

    Quote Originally Posted by Houston View Post
    Mr Bruty, its got nothing to do with luck, its all in the prep!


    Houston did you by any chance, do a Bal course? just curious.

Similar Threads

  1. Restricted height flooring problem
    By vetinry in forum Tiling Forum
    Replies: 4
    Last Post: 17-06-2010, 07:23 PM
  2. electric UFH and insulation question
    By Mark B in forum Electric Underfloor Heating
    Replies: 9
    Last Post: 19-04-2009, 08:54 AM
  3. Electric UFH vs Wet UFH - My Verdict
    By ralsmith1 in forum Electric Underfloor Heating
    Replies: 9
    Last Post: 18-04-2009, 04:23 PM
  4. First UFH Job
    By tay1974 in forum Electric Underfloor Heating
    Replies: 2
    Last Post: 19-03-2009, 10:32 AM
  5. Reducing floor thickness with UFH
    By nell in forum Electric Underfloor Heating
    Replies: 29
    Last Post: 10-03-2009, 01:27 PM

Visitors found this page by searching for:

floor transition height

adjacent floors of different height

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Tilers Forums is the UK's largest wall and floor tiling forum. Advice is provided free of charge to all users. Tilers Forums does not take responsibility for any loss or damage caused due to following advice found on this forum. All wall and floor tiling should be carried out by a qualified wall and floor tiler. Views expressed on this forum are of the users and not Tilers Forums. Views expressed on this tiling forum are of the contributor only and not the forum as a whole. Not all views should be taken as fact but simply the opinion of the person posting. Readers are reminded to seek professional advice before undertaking any wall and floor tiling project.

Tilers Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.
DMCA.com
[Output: 221.42 Kb. compressed to 197.62 Kb. by saving 23.80 Kb. (10.75%)]

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28